Distribution and use of electricity throughout the home. Electrical standards vary greatly worldwide, so providing your location in your question or your profile helps ensure you get answers that are relevant to you.

learn more… | top users | synonyms (1)

3
votes
1answer
8k views

Is it safe to cut and put a compression end on a live cable TV wire?

Just moving into a new US location. The location has both Verizon and Comcast available. I am trying to use Comcast. The Verizon installer appears to have cut the Comcast cable that went to an ...
2
votes
2answers
4k views

Why does my GFCI receptacle trip when I connect the load wires?

I was trying to install a GFCI outlet and when I install it with the five wire setup with the line on top and load on bottom, the outlet continually trips. I made sure which wire was the hot-line and ...
6
votes
4answers
30k views

Is it safe to install a three pronged wire into a four pronged dryer?

I just moved into an old home that has a three pronged wall jack as shown below: I have a newer dryer that has a four pronged wire. Please see the back of the dryer, I've removed the four pronged ...
1
vote
1answer
2k views

Can I steal a neutral wire from another circuit?

I have some Z-wave light switches that I want to install; below is a link to the diagram for the light switches. Basically I can have all the wiring completed minus the neutral wire for the switch at ...
1
vote
1answer
5k views

How can I safely remove one baseboard heater out of a set of two?

I have two baseboard heaters on either side of my living room. They are both on the same breaker and connected to the same thermostat. The breaker looks like it takes up two spots and has a 20 on the ...
0
votes
4answers
12k views

How can I use a separate transformer to provide a C wire to my thermostat?

I Purchased the Honeywell WiFi Prog Thermostat to replace my Round Digital Honeywell Thermostat. I have separate Heating and Cooling (Heating is a Weil McLain Boiler for Hot water baseboard and Hot ...
6
votes
3answers
4k views

Why is it OK to use a 50 A receptacle on a 40 A circuit?

NEC's Table 210.24 " Summary of Branch-Circuit Requirements" shows required condudcor and outlet requirements for different circuit ratings: Why is it permitted to put a 50 A receptacle on a 40 A ...
10
votes
1answer
1k views

What are “termination points” and why do I need them on my electrical supply?

An inspection of my electric supply service on the outside of my home in Maryland said I need 3 termination points and two grounding rods. The grounding rods I can get but I have no clue about these ...
11
votes
6answers
46k views

Should I put a dimmer switch on a ceiling fan?

I have a ceiling fan on our bedroom's vaulted ceiling. Since we don't want 7' pull-cords, the speed is stuck at full-tilt, which is no good. The fan has separate switches on the wall for lights and ...
2
votes
1answer
5k views

What are the codes for electrical wiring in attics?

What is the typical code for wiring in attics? I understand these vary but what's best practice? Can you just have electrical wires exposed with all the junctions, in junction boxes, provided all the ...
4
votes
4answers
3k views

How can I wire this three-way circuit between two buildings with only 3 conductors?

I am rewiring my entire house after a major malfunction of two antique knob and tube circuits. I'm up against a challenge with some outdoor lights. Here's the situation: I have a detached garage. It ...
2
votes
1answer
7k views

Why is my electric hot water heater producing lukewarm/cold water?

Yesterday after returning home from work I discovered my hot water is not working. When you turn on the faucet (any in the house) just a little warm water comes out and then it turns cold. I checked ...
7
votes
5answers
67k views

Can different gauge wiring be used in the same circuit?

I am extending a lighting and outlet circuit in a basement. The current setup has the following characteristics 15 amp. circuit breaker (200 amp service) 4 existing lighting fixtures using CFL bulbs ...
2
votes
1answer
452 views

Can I connect wall sconces to an existing switched circuit?

My den has four outlets tied to one wall switch (top receptacle at each outlet). I am looking to install four sconces (two per wall on two walls) and was wondering if I can tie these into the existing ...
2
votes
2answers
357 views

Where does the excess electricity from my solar panels go?

When my excess electricity goes back into the grid, where does it go after it has passed through my meter? Does it go to the next closest house needing power?
1
vote
1answer
183 views

How do I select the right generator?

I'm looking for advice on what kind of generator I should get for my mobile home. We have had 3 pretty bad storms (2 hurricanes, 1 blizzard) and am looking to give my home backup power. Now I have ...
0
votes
1answer
558 views

How can I wire multiple recessed lights and multiple dimmers?

How do I wire recessed Zinc Alloy ceiling lights. There are eight lights and eight dimmers. Can I run all wires and the feed into a junction box?
1
vote
1answer
2k views

What is causing my light bulbs to burn out so quickly?

I have some 12-volt outdoor lighting that is quickly blowing through light bulbs (couple weeks at a time.) I just measured the voltage and it read 13.4 volts. Could this be the culprit? The other ...
2
votes
2answers
14k views

Should I use 3 wire or 4 wire for a range?

I am trying to do a little work and have an electrician check it. I have a range that is a 3 prong 50amp 125/250 (looks like the 10-50R). List of materials purchased: 50 amp Siemens Circuit ...
3
votes
2answers
417 views

How do I rewire this circuit controlling several lights and receptacles?

The wiring is suspended on the ceiling inside a metal tube that connects to each light socket and set of outlets at independent metal junction boxes. The first light in the chain finally stopped ...
1
vote
3answers
3k views

Why is an AFCI tripping when a particular light on a different circuit is turned on?

I have 4 GE AFCIs in a GE subpanel in my basement. Occasionally, when I turn on a bank of dimmable CFL lights via a CFL-rated dimmer switch, I get a trip in a particular AFCI breaker that's on the ...
2
votes
1answer
2k views

Can I replace a single light switch with a 3-way switch that can individually control 2 lights in a fixture?

I have a ceiling light fixture with 2 bulb sockets. Right now it's controlled by a single 2-way switch (on/off). My idea was to install a 3-way (or possible 4 but not necessary) switch that can ...
0
votes
1answer
8k views

What could cause a ceiling fan to lose rotation speed?

I have two identical ceiling fans in my house that were installed around 4 years ago. One no longer rotates as fast as it used to at top speed. At a guess I would say it has lost 30 or 40% of its ...
4
votes
1answer
3k views

What are possibilities of balancing 3-phase consumption?

A lot of homes have a 3-phase electric connection. Each of the phases has some appliances connected to it. That implies power consumption in any moment on each phase is different, so we have an ...
3
votes
2answers
474 views

Can I replace an old closet light with multiple electrical outlets?

I have asked a family member to replace an old light fixture in a large walk in closet with an actual electrical strip. The house is an 101 year old craftsman. There aren't any electrical outlets in ...
6
votes
1answer
21k views

How can I install this programmable switch where a neutral is not present?

I'm trying install this programmable switch but the instructions do not match reality. The instructions refer to the existence of a black (load) cable and a white (neutral) cable supposedly coming out ...
6
votes
3answers
5k views

Is it OK to have ground wire connected to breaker box wall instead of neutral bus?

After having issues with lights flickering, I noticed the main 100A breaker was warm and arcing slightly. Instead of just replacing the breaker, I decided to call in a electrician to install a larger ...
0
votes
1answer
381 views

How can I install this automatic transfer switch?

I currently have a Gentran 3028 subpanel connected to a 12,000 watt generator over a 30 AMP branch and the utility/main panel over a 60 AMP branch. I want to replace the Gentran with a APC UTS10BI. ...
3
votes
1answer
3k views

How can I install this programmable switch?

I just had our house re-wired (by a professional, not myself). I'm looking into replacing a light switch with a fancy programmable version (Honeywell Econoswitch RPLS740B). The location for the ...
1
vote
2answers
1k views

How can I install 3 way switches that cut power to several 2 way switches?

I'm rewiring my unfinished basement. It has two entrances - a cellar door to the outside and the normal staircase in the house. Even though it is unfinished, the basement is kind of divided into ...
3
votes
3answers
2k views

How can I shut off circuits when I have a generator with an automatic transfer switch?

We had professionals install a generator with an automatic transfer switch. I showed them our circuit-breaker box and told them which circuit numbers should be on generator power. Okay, everything's ...
7
votes
1answer
6k views

What is a split bus panel, and how do I recognize it in the field?

I'm having trouble identifying a split bus panel. I design and install Solar systems, and lately (after Mr Wiley gave a few seminars to local inspectors) the local authority having jurisdiction (AHJ) ...
1
vote
1answer
5k views

Why is my electric circuit breaker tripping?

For the past 4 days our circuit breaker has tripped several times a day. On the box each fuse thing is labeled i.e. "Upstairs lights", "upstairs sockets" etc. Now normally if we have had a blown fuse ...
3
votes
1answer
20k views

How can I split my rg6 cable runs without losing my signal?

So I've been working on this for months as I finish my basement. We don't have cable tv or satellite. We just get broadcast tv using a digital roofmount antenna and then in the house a digital ...
-3
votes
1answer
383 views

How can I install a new bathroom GFCI receptacle? [closed]

How can I install a bathroom GFCI, by connecting it to another outlet?
4
votes
2answers
4k views

How does 4-quadrant metering of 3-phase electricity work?

I have a 3-phase 4-quadrant electricity meter installed because I have a photovoltaic plant on the roof of house. A 4-quadrant electricity meter means it can measure both consumption and generation of ...
2
votes
2answers
2k views

Should I be able to run some 1.5" PVC chase conduits from attic to basement next to a cold air return?

I have a new home I just moved in to and rather than having them put this stuff in ahead of time (silly me) I'm now trying to do it now. Here is my situation... I live in a 2 story home with a ...
1
vote
0answers
244 views

What could cause neutral wires in my service panel to read 120V?

I have a 200 A service panel with 12 breakers. Seven of the breakers work fine. There are 5 other lines that come in. When I hook up the black wires to the breakers and turn them on I get a charged ...
1
vote
0answers
32 views

How to verify if the protective earth/ground is separated from the neutral wire in an electrical AC installation? [duplicate]

Possible Duplicate: How to verify if the protective earth/ground is separated from the neutral wire in an electrical AC installation? It's easy to verify which wire is the phase without ...
3
votes
4answers
7k views

How can I verify that the protective earth/ground is separate from the neutral wire in an electrical AC installation?

It's easy to verify which wire is the phase without relying on wire colors. But I'm not sure if I'm able to determine which wire is the ground and which is the neutral. I have heard that using a ...
3
votes
1answer
759 views

How do I run a dock circuit and what size breaker will be needed?

I am running 10 gauge wire to my dock which will be about 100 ft from the disconnect box on the house to the dock. I will be providing electricity to a 1/2 hp hoist, which runs on 110, that will only ...
1
vote
1answer
815 views

How can I replace my old dimmer switch?

Replacing dimmer. Old dimmer has two black wires attached to two white wires in box. There are two black wires in box not attached to dimmer but wire-nutted together. Is it ok to wire the new dimmer ...
0
votes
1answer
230 views

What are these electrical boxes in the closet that have no breakers in a house with buttons for the light switches?

My mother's home has these metal panels in the closet on the second floor, directly under them on the 1st floor is the breaker box. The house has push buttons for the lights instead of switches. There ...
21
votes
9answers
42k views

How should I go about installing a 12 volt DC residential circuit?

I have a couple deep cycle batteries that trickle charge from a solar panel, for emergency use. Right now the only way I get useful power from them is to use a 12VDC -> 120VAC inverter, e.g. the type ...
1
vote
1answer
910 views

How can I wire an HD antenna into my attic?

I have a 2 year old house 2 floors and then an attic that you have to use a pulldown to get into. The house has an ethernet cable (90% sure it is an ethernet cable) that is in the attic, I have a HD ...
1
vote
2answers
5k views

Does a single-gang double timer switch exist?

I have a single gang outlet that current has a double/split switch installed controlling an inside light and an outside light. Ideally I'd like to have the outside light on a timer. Does a single ...
1
vote
2answers
133 views

What kinds of dimmers do I need?

I'd like to make myself a lighting control that would schematically look like this: I don't know a lot about dimmers, but I heard they have some parameters which might prevent them from working. ...
10
votes
3answers
592 views

How should I rewire this situation?

In my dinning room, I have this: There is a wire run going up through the floor from the basement. It then goes outside the wall, around a stud (or studs, I'm can't tell there is more than one), back ...
4
votes
2answers
1k views

Can I install a light between two three-way switches?

is it possible to add a light to a three way switch circuit between the two three way switches (ie can i tie into the three wire connecting the two switches in anyway to make them work the new light ...
3
votes
1answer
9k views

How do I wire a receptacle and a light switch?