3
votes
1answer
30 views

When replacing non-grounding type receptacles is a GFCI receptacle required, or can any GFCI device be used?

Under the NEC (it was 210(7)(d)(3), but appears to have moved around some), it is permissible to replace an ungrounded receptacle with a GFCI receptacle, then wire further ungrounded or non-grounded ...
2
votes
3answers
96 views

Can I use a 50 amp GFCI breaker on 15 amp circuit?

I am in the process of changing my hottub over to wood heat. I have eliminated all controls and am running the pump directly from the panel on a double 15 amp breaker (240 volts). I have my existing ...
0
votes
2answers
78 views

How to wire GFCI outlet

The bathroom includes a GFCI outlet that will not reset. Research revealed that such outlets do seem to stop working sometimes. So I am attempting to replace the outlet. After pulling the faceplate ...
0
votes
2answers
56 views

What does it mean when one wire goes into load, and one goes into line

I am replacing my kitchen outlets with GFCI. The inspector told me I just needed to install one at the first outlet in the circuit. I looked at the outlets on either side of my kitchen; at one end ...
0
votes
1answer
25 views

Pool pump plug trips when GFCI outlet receives power

I have a GFCI outlet out by my pool. I have a timer switch inside that sends power to that outlet. My pool pump has a plug that is GFCI (I assume that is what a plug is called it has a test and reset ...
0
votes
2answers
65 views

Use of combination CAFCI and GFCI breakers instead of recepticles

I am about to begin a project that will include one or two new circuit for outdoor lights and receptacles attached to the main building. I will probably installing a new home run line from the panel ...
2
votes
1answer
65 views

How do I wire a GFCI switch/outlet receptacle?

I'm replacing a switch with a switch/outlet (GFCI) in my bathroom. The switch will control the bathroom exhaust fan. Currently I only have two wires to work with (hot & neutral...no ground). ...
0
votes
1answer
58 views

How do I properly install GFCI outlets with existing 12/3 wire in parallel and on a switch?

I am trying to help my inlaws with a problem in their living room. Two of their outlets stopped working and I don't really know why. The outlets were wired to a switch in the hallway, which ...
1
vote
1answer
46 views

Is a weather resitant gfci required outside in a metal box with in use cover?

I have a pool that is just off my deck. The gfci i have went bad so i need a new one. It was a 15 amp gfci in a metal box attached to 1/2 in emt conduit with a metal box and a non in use cover. Thi is ...
0
votes
1answer
103 views

Why do I have a green light on my GFCI but the outlet will not come on?

While cleaning, my niece sprayed my GFCI outlet causing it to go out. I attempted to reset it but came up with negative results. I purchased another one, hooked it together (green light came on ...
0
votes
0answers
74 views

How do I wire a GFCI with 5 wires?

How do I install a GFCI receptacle with 2 black and 3 white wires plus a ground? I have two such regular receptacles next to sinks and should replace them before the upcoming home inspection, please ...
0
votes
0answers
89 views

Why is my bathroom vent fan tripping the GFCI when being shut off?

I have a GFCI tripping when a vent fan is being shut off. I saw in KeithS's answer to a similar question that the blades rotating after shut off causes an imbalance, tripping the GFCI. In my case the ...
1
vote
2answers
388 views

Why does my fluorescent ceiling fixture trip the GFCI sometimes?

Every so often, roughly a 1/20 chance, flipping the light switch to my laundry room's fluorescent fixture will trip the nearby GFCI outlet. Why is this? Is it more likely to be the GFCI being faulty ...
5
votes
3answers
564 views

GFCI outlet hot when nothing's plugged into it

Using a thermal camera (coolest thing in the world, by the way), I discovered that a GFCI outlet in my bathroom is hotter then the surrounding wall when nothing's plugged into it: It's not boiling ...
5
votes
3answers
152 views

Does big current draw make GFCI outlets go bad?

About 2 years ago during a kitchen update, I replaced a GFCI outlet with a new one, 20-amp (both pass through and the GFCI outlet itself). Branching downstream from it are two more outlets, one on the ...
2
votes
2answers
120 views

What could have caused my GFCI to trip, and what can I do about it?

About a week ago, a GFCI tripped. I noticed that because appliances in my kitchen stopped working. The short story is that something was put into an outlet that shouldn't have been. That's not the ...
2
votes
1answer
114 views

How can I repair a ground-fault?

I'm hooking up a new GFCI in a remodeled bathroom, replacing an older one. There are two outlets following on the circuit. The GFCI works fine, but as soon as I would plug a light into the next ...
0
votes
2answers
81 views

None of the outlets in the kitchen are working

The other day I switched on the garbage disposal and now none of the outlets in the kitchen work. This circuit is GFCI protected from the panel but the GFCI breaker in the panel is not tripping. When ...
1
vote
2answers
256 views

GFIC requirements for a Kitchen multi-outlet strip

I was thinking of replacing my current kitchen counter receptacles with a Hard Wired Multi-Outlet strip that would run below my cabinets. My question is How would I provide GFCI protection? Can a ...
2
votes
1answer
168 views

Replacing outdoor outlet

How can I replace an outdoor outlet cover that has a stripped center screw? Do I need to replace the outlet as well? Do I need to replace the box that the outlet is housed in if it is coming out ...
0
votes
0answers
85 views

Why don't I have power at my GFCI outlet?

Sorry for what will likely be a long question! It all started with a bathroom light that would not turn on, even though the bulb was good. I decided to get my multimeter and see if the switch was ...
2
votes
2answers
169 views

Did I damage the breaker by incorrectly wiring a generator?

During a power outage I attached my generator incorrectly (I have never done this before - I just was not paying attention). Anyway, I crossed the ground at the box with the black. When I turned on ...
3
votes
2answers
1k views

How can I find the first receptacle in a circuit?

I know how to wire a GFCI receptacle and all the things to go with it in doing so. But what I do not know is the following. I understand the GFCI receptacle should be first in line to protect the ...
2
votes
2answers
5k views

How can one whole group of outlets stop working, but the wires to one plug on one outlet are still hot?

I have a bank — circuit? — of outlets in the kitchen that have stopped working. One of these outlets is a GFCI but it is not tripped. The breakers for all the kitchen outlets have not tripped but I ...
0
votes
0answers
80 views

Why does a GFCI breaker and receptacle on the same circuit cause tripping tripping?

I work in the apt industry as maintenance, currently on a new property. I had a call this weekend about no power in kitchen outlets or dining room. I found a GFCI outlet in the run, tried resetting it ...
3
votes
1answer
175 views

How can I provide GFCI protection to my kitchen receptacles?

I Live in Round Lake, Il., in a 1940's built home. In my kitchen I have four counter top receptacles surrounding my sink area. Two of the receptacles are close to the sink, and I want to replace them ...
2
votes
1answer
232 views

What size GFCI and receptacles on 20A circuit?

I am adding a string (5-6) of receptacles to an existing 20A circuit in my basement that currently has just one 15A duplex receptacle on it (with 12/2 Romex). I am planning to replace the existing ...
1
vote
1answer
440 views

Can I install two GFCI receptacles on a multiwire branch circuit?

I am wondering if I'm using a 10/3 teck cable to power two 20 amp GFCI receptacles for a temporary power situation, can I use two separate single pole 20 amp breakers at the panel for each receptacle. ...
4
votes
3answers
1k views

Should I use a GFCI or AFCI circuit breaker with knob and tube wiring?

My American house was built in 1942, and much of the wiring is still knob-and-tube wiring (2-wire, no ground). Over the years new modern wiring has been added to the house, but we still have some KnT ...
6
votes
7answers
390 views

What could be tripping multiple GFCI breakers?

I have 14 ground fault circuits split 7 on each side of my panel. I have recently had 5 or six trip on the left side and 1 or 2 on the right. It happens at all hours. It appears I have some kind of ...
3
votes
1answer
2k views

Sump Pump Trips GFCI Receptacle. Is a single, dedicated non-GFCI receptacle safe?

I recently replaced my sump pump in one of my two sump pits. To comply with codes, I replaced the outlet with a GFCI type outlet. Unfortunately, once I turn the power back on, the GFCI trips ...
0
votes
0answers
26 views

dual GFCI circuits with multiple protected outlets, all sharing a neutral [duplicate]

I'm trying to wire two GFCI circuits sharing a neutral. The line is coming in from a 2-pole circuit breaker. I want to have two circuits at each location, each protected by a GFCI upstream. ...
3
votes
2answers
1k views

Why does a GFCI trip when anything is plugged into the other outlets?

There is one outlet with the GFCI and several other outlets without. The GFCI outlet works fine, while anything plugged into the other outlets causes the GFCI to trip. How should I detect and fix ...
5
votes
1answer
821 views

What problems could occur if I plugged a 3-prong plug into a receptacle labeled “No Equipment Ground”?

I have several old, ungrounded outlets in my house which are protected with GFCI, which is allowed per code as the GFCI will protect a person in the event of a ground-fault. These outlets are ...
1
vote
0answers
265 views

Why do I have a 3 wire/double pole breaker for kitchen receptacle?

I am switching my kitchen receptacle to a GFI; it has 3 wires. I'm pretty sure I have to break the bar between the two hot screws, thus making the top and bottom on a separate circuit. What is the ...
1
vote
0answers
153 views

Washer tripping gfi outlet

I've been living in my house for almost two years and my washer and dryer have been working fine. I have a maytag Neptune washer and dryer, just the other day I took a packet of tide washing machine ...
2
votes
2answers
393 views

Will a GFCI device work on circuit where the neutral is switched?

How well will a GFCI circuit be able to detect current flows, if both the "hot" input and the (supposedly) "neutral" input to a GFCI outlet are energized? The reason I am interested in this is that I ...
1
vote
0answers
202 views

How to finish the wiring of a shared GFCI receptacle

My neighbor who is an electrician helped me start an electrical project in my garage but has been MIA for 3 weeks and I'm not sure how to finish the wiring of the receptacles. He didn't seem to start ...
2
votes
2answers
265 views

Why is my GFCI receptacle tripping when I add another receptacle to the circuit?

I have 3 receptacles in my garage. One is a GFCI which protects all 3 outlets. I want to connect a new receptacle off the third receptacle (end of run) on other side of wall, and have it protected by ...
2
votes
1answer
131 views

Does this wiring sound right?

First let me preface this by saying that I am very comfortable doing basic electrical work. With this project my electrician is on vacation and won't be back for a few weeks but I wanted to see if I ...
2
votes
1answer
359 views

How can I prevent the receptacle in my yard from tripping the GFCI used to power my sprinklers?

I have a GFCI in garage that protects one receptacle in the garage and one in the yard. The GFCI receptacle itself feeds the sprinkler timer. The other receptacle in the garage is hardly used. The ...
4
votes
2answers
719 views

Why does my GFCI trip when I plug things into load side receptacles?

I installed a new outdoor circuit. The line comes out of the house and into the LINE side of the GFCI outlet. I connected a wire to the LOAD side and ran it to two standard outlets downstream. My ...
3
votes
1answer
855 views

How do I wire a GFCI to provide continuous power to a dishwasher and switched power to a garbage disposal? [duplicate]

I am replacing a regular three pronged outlet with a GFCI for my disposer and dishwasher. There is a white, black, red and ground. How do I install it so as to keep constant power to the dishwasher, ...
1
vote
2answers
2k views

Why isn't my GFCI receptacle working?

I am installing a GFCI outlet and I am having some issues. I have identified the hot and neutral wires. They test positive with the voltmeter when I turn on the switch. I connect the receptacle to ...
1
vote
1answer
801 views

What could be causing a new 20 amp dedicated circuit supported by a GFCI breaker to trip?

I installed a dedicated 20amp circuit home run to support a single duplex outlet in a bathroom. The GFCI breaker is wired correctly. However, When I plug in a load such as a light a the breaker ...
2
votes
3answers
1k views

How to independently switch a GFCI outlet?

I would like to add a plug outside where each plug would be independently switched. The use of this is to be able to switch a rope light and a fan separately. This is being added to a new breaker so ...
3
votes
3answers
4k views

How do I wire a GFCI receptacle using two black wires and two white wires?

I recently purchased an older home and wanted to install GFCI outlets in the kitchen. When I opened up the outlet, there were four wires (two black and two white) in addition to the ground. I ...
2
votes
3answers
941 views

How can I remotely monitor a GFCI receptacle?

How can a sump pump in a crawl space only accessible by crawling down a hole in a closet have its GFCI protected outlet monitored from the living room? I am imagining the best way to run the pump is ...
1
vote
1answer
293 views

Can I have GFCI receptacles on the same circuit as normal receptacles? [duplicate]

I am looking at a few books and they all show samples of circuits, but never tell or show if you can mix receptacle types. I have a circuit running to 2 bedrooms for my power outlets. The are on 12/2 ...
4
votes
3answers
3k views

Why does my circuit breaker trip with any small load, even after replacing the breaker?

I have a 20A 240V GFCI breaker in my main breaker box going to a conduit to another breaker box outside. All worked well last summer. Now, when I put any load (weed-eater, light, etc.) on an outlet ...