2
votes
0answers
39 views

Is it ok by code to enclose a residentail breaker box in a finished basement as long as there is an access door and what are the requirements? [duplicate]

I am finishing a basement and want to enclose the 200a service box and wiring with a framed cabinet of some sort. Is there any requirements for clearances and what you can enclose it with? I am in ...
4
votes
1answer
158 views

Can I install a receptacle outlet below a window?

I need to add a receptacle outlet to an existing line. I will run the line from an existing receptacle outlet. Is it okay to locate the new outlet below an existing window?
4
votes
2answers
110 views

Is it okay to protect NM Cable in an unfinished basement with ENT?

Adding a 20 amp subcircuit (120V) to furnace room to turn it into a workshop. Initially it will have one duplex and 2 fourplex receptacles, the fourplex receptacles will be on cement walls, the duplex ...
4
votes
1answer
129 views

What should I do about old cables that have been damaged?

I was replacing some drywall and noticed the wiring underneath has a couple of surface tears. House is from the sixties, but has been rewired with new Romex, except this circuit. Wire seems to be old ...
1
vote
1answer
109 views

Is it acceptable to splice a circuit in two opposite directions for outdoor recepts/lighting?

Per the 2011 NEC, is it acceptable to... Splice a circuit (using a junction box indoors) as long as I leave it exposed, use the correct wire connectors, and have it covered? Use this run one side ...
-2
votes
1answer
90 views

Residential electrical installation, at what voltage is a licensed contractor required?

I'm trying to figure out regulatory requirements for residential electrical installations. Specifically, when is a licensed electrician required by code to perform an installation? Obviously you don't ...
2
votes
1answer
87 views

How to reroute a circuit that goes through a return air plenum

Old house, need to replace a wire where the insulation has been stripped off from when the original installer pulled it through a joist. Normally I'd just follow the original path of the old wire, ...
1
vote
1answer
85 views

Do smoke detectors have to be hard wired in New Jersey?

I'm rebuilding after a fire, and I need to know if the new smoke/co detectors need to be hard wired.
5
votes
1answer
152 views

How can I replace 2-prong receptacles in a code compliant way?

I have some 2-prong non-grounding type receptacles, and I'd like to replace them with 3-prong grounding type receptacles. According to National Electrical Code, what are my options?
1
vote
2answers
89 views

What's the proper procedure for replacing ungrounded circuits?

I have a house that has several ungrounded circuits that uses the older 2 wire romex (pvc insulation, black woven jacket). I'd love to have AFCI protected circuits for the bedrooms, and grounded ...
5
votes
1answer
438 views

How many cables are you allowed to run through a single hole in a wooden floor joist?

How many cables are you allowed to run through a single hole in a wooden floor joist? For example, could I run five 12-2 cables through a 1-1/8" hole? I know they physically fit, but is there a code ...
5
votes
2answers
630 views

Can I wire a refrigerator and dishwasher on the same circuit?

Can I wire a refrigerator and dishwasher on the same 20 amp circuit?
3
votes
2answers
368 views

Can I terminate a ground wire to the neutral bus if the ground bus is full?

I have a Crouse-Hinds main load center. The ground bus is at the top left of panel and the neutral bus is at the bottom right of the panel. I want to add a 15 amp circuit for two outlets in my ...
1
vote
2answers
168 views

Can I mix 12 gauge and 14 gauge wire in the same 15 amp circuit?

I have 12/3 wire from a switch to 3 light fixtures; can I feed the switch with 14/2 wire from a 15 amp breaker?
2
votes
1answer
93 views

What are the code requirements for installing a ceiling fan alongside a fire sprinkler?

I have a fire sprinkler in my bedroom ceiling which is right in the middle. I want to install a ceiling fan. What are code requirements to follow?
2
votes
3answers
187 views

Any problem with installing two identical circuit breakers in series?

Suppose I want to reduce risk of a circuit breaker malfunctioning and failing to disconnect a shorted circuit. What if I install two identical breakers sequentially (one after another) so that if one ...
3
votes
2answers
162 views

Does NEC allow for recessed lighting to be placed in a vertical wall?

I am about to start running electrical in my bathroom remodel and I am considering options for lighting. I have a wall on one side that has 5.75" of space (this was for recessed shelving in an ...
0
votes
2answers
102 views

Are electrical subpanels safe in the bedroom?

If not, how do you correct it, or can it be moved without making too much work?
1
vote
2answers
152 views

Is it code to have electrical wire going no where?

I have a wall open in the center of my house. I am going to run some 14-2 up it and and to about 5 feet from my panel, leaving plenty of extra wire to hook up in a few months. On the other end I am ...
5
votes
2answers
789 views

How do you secure electrical outlets in a concrete block wall?

I have an old home that has several outlets in the exterior wall. These outlets are not secured to the block, they just dangle in the opening and are only secure (or appear to be firmly in place) due ...
1
vote
0answers
78 views

Can I attach a metal box for a vanity light to a wood cross?

I am redoing a new bathroom. I have a metal electrical box that I want to replace (because it is an odd size from the 50s). The current one is simply screwed to a wood cross (2x4) running ...
0
votes
2answers
111 views

According to NEC 2008 can you use non-metallic boxes in framing that transports environment air?

In the Home Owner's electrical test, the term "environmental air" is used. What does this term mean, and where is it defined? and can you use a non-metallic box? Also when reading the question do ...
1
vote
2answers
209 views

What do I need to know before taking the home owner's electrical test?

Inspector came over and checked out my basement today. He suggested that I take the `local home owner's electrical test to sign off on that part of the permit. They give you the NEC 2008 handbook, ...
1
vote
1answer
353 views

Can I connect the generator neutral to my mains neutral permanently?

I have a 3 phase 15KW generator with four wires. I want to use it as a standby generator for my house. My house uses 1 phase 220 volts on two wires (no ground as the house is quite old). I have a 3 ...
2
votes
2answers
179 views

What type of wiring should bedroom overhead lighting have?

On the phone with a friend in Cali this morning. He said that some municipalities are requiring /4 (12-3 or 14-3 romex) wiring for all new construction or rewiring for overhead lighting components. ...
2
votes
3answers
183 views

Is it safe/compliant for one circuit to supply grounded wall outlets in both a kitchen and a living room?

On one side of my wall (in kitchen, not the refrigerator or stove plug) is a three prong grounded outlet. Would it work without overloading a circuit to put a new outlet on the other side of the wall ...
2
votes
1answer
198 views

Can I run an unrelated electrical cable under a bathtub?

I have an older house with a mixture of grounded and ungrounded outlets. Every room has at least one grounded outlet in it, except one. I've long wanted to run a new cable to that room and at least ...
3
votes
1answer
3k views

How do I properly ground my subpanel that only has one neutral/ground bar?

I am adding a sub panel in an unattached building. My sub panel has the connection for the 2 hot wires coming from the source panel (a 40 amp double breaker) In addition it has one neutral/ground bar ...
1
vote
2answers
480 views

Can I install lights on a 20 amp circuit that has receptacles already wired?

I have never been able to ask the following question and get a simple straight answer and would like to know why there is a controversy, and what the answer really is. The question: Can a 20 amp 12 ...
6
votes
2answers
151 views

Do exterior duplex electrical receptacles have to be on multiwire branch circuits?

I have an exterior receptacle on my house, and it is currently taking up 2 circuits (similar to kitchen counter plugs). Is there any code/regulation that indicates exterior receptacles must be on ...
5
votes
1answer
203 views

What is “workmanlike manner”?

I have to ask this because I have been doing a ton of electrical work in my house. Will get inspected soon. I am pretty neat - everything is stapled uniformly and ran at the same height- but I ...
5
votes
1answer
2k views

How can I mount an 12V transformer for LED lighting inside a wall?

The stairs to my basement has one light fixture at the bottom, and that casts a shadow on the rest of the stairs. I want to run a strip of LED lights up the crown molding or on top of the upstairs ...
3
votes
2answers
2k views

Does it matter if I mix neutrals and grounds in the main panel?

Code question here. I do a lot of electrical and like to follow code exactly. I have done pretty much everything but hook up lines to main box. Taking a stab at it this time. First I see that I ...
3
votes
1answer
259 views

How do I string a low voltage wire between two buildings?

I need to get Cat6A to an outbuilding for network communication; underground is not an option. I think I have an idea on the method: grounded pillars with a guyline and the outdoor cable. What NEC ...
2
votes
2answers
1k views

Can I extend the ground/bus bar in a main service to accomodate subpanel equipment ground?

I am about to replace the main service breaker panel in my house. The old panel (a 200amp Siemens 40-circuit) had bus bars that extended the entire vertical length of the box. The new panel I would ...
1
vote
2answers
1k views

What is code for installing a dishwasher in the U.S.?

I will be replacing my dishwasher and I am curious what is the current code for the wiring of the dishwasher.
5
votes
2answers
3k views

Is it code-legal to have a circuit breaker box within a storage room?

I am currently in the process of planning a room remodel to convert an existing bedroom into a home office and storage room. One thing that makes this conversion a little bit tricky, is the existence ...
2
votes
1answer
2k views

What are the codes for electrical wiring in attics?

What is the typical code for wiring in attics? I understand these vary but what's best practice? Can you just have electrical wires exposed with all the junctions, in junction boxes, provided all the ...
5
votes
4answers
9k views

Can different gauge wiring be used in the same circuit?

I am extending a lighting and outlet circuit in a basement. The current setup has the following characteristics 15 amp. circuit breaker (200 amp service) 4 existing lighting fixtures using CFL bulbs ...
1
vote
0answers
134 views

How do you plug an unused hole as per the NEC for a liquid tight enclosure?

I have been looking for a way to seal a liquid tight product using Listed blanking plugs / Cap-offs or similar to comply with the NEC (US National Electrical Code). We wanted to use Conduit Entry ...
1
vote
1answer
439 views

Is there a required spacing between where high and low voltage lines attach to a house?

If both the high and low voltage lines are strung from the pole to the house, is there a minimum spacing required between where they anchor to the structure? The AC lines enter through the ...
7
votes
3answers
6k views

Are generator interlock kits permitted in residential applications?

There have been some questions on the site lately, that reference using interlock kits with portable generators. This has inspired me to read through article 702 Optional Standby Systems of the ...
3
votes
1answer
255 views

Are four gang plastic boxes stackable in a wall?

I would even be willing to go side by side but I would like to stay with the four gang sizes. I am hoping this would pass code and would prefer to stack so if there is someone that knows if it is ...
2
votes
2answers
1k views

What is the purpose of a double pole breaker for separate 15A circuits?

My new house is done being built and I am going to come in and install my new gas range and dishwasher, both 120V 15A appliances. I got thoroughly confused looking at the breaker box because gas ...
4
votes
1answer
352 views

Is it against code to secure junction box using Liquid Nails?

I need to extend a 14/2 WG wire a few feet. To do this I want to add the extra wire using a junction box. The problem is that I can't get a good angle to nail the junction box down so I was wondering ...
6
votes
2answers
2k views

Is it OK to have a 20 Amp receptacle on a circuit with 12 AWG wiring and a 15 Amp breaker?

I have a hypothetical question: If you have a 15 Amp breaker connected to a 20 Amp T type outlet with (20 Amp) 12 AWG wire, is it within code, below code, or above code, where code means the National ...
3
votes
1answer
219 views

Two switches in same box, on different circuits

Is it acceptable by US NEC standards to have two switches in a double wall box that operate on entirely different circuits in a late 50's house?
5
votes
1answer
254 views

Can a single metal electrical box use two ground clips?

Inside a metal electrical box, can I use multiple ground clips (one for each conductor), or is it required that all ground conductors be twisted together and pigtailed into the same clip?
5
votes
2answers
3k views

Is there any acceptable way to cover a junction box?

The outlet for my range hood was misplaced. It needs to be 4 inches to the side. I can make the junction and move the wiring to the new location but I really don't want to have the empty plate ...
3
votes
2answers
594 views

What kind of light can I install in a small, low-ceiling coat closet?

Our Northern California house has a small coat closet (really a hallway with 2 doors and hooks for coats) between our front entry-way and our basement. It's a tiny space: 3 feet wide, 5 feet deep, and ...