The tag has no wiki summary.

learn more… | top users | synonyms (2)

0
votes
3answers
33 views

Re-use circuit breaker handle tie?

I have a double pole 30 amp breaker controlling a 230 volt load that I need to replace. I cannot obtain one at this moment; perhaps tomorrow but maybe next week. Either way, I have two good used 30 ...
1
vote
2answers
36 views

Insulating near a breaker box

Hello: In remodeling my basement I have so far finished installing R-10 2" XPS insulation against my block walls. My question is: How close or how far away from the circuit breaker panel can I place ...
0
votes
1answer
95 views

Which thermal circuit breaker should I buy?

I live in a small house in Argentina where we use 220 volts. I have a thermal circuit breaker that do squeak noises when the iron starts or the fridge starts. I adjusted the four screws of the breaker ...
2
votes
2answers
113 views

Can a laptop cause an AFCI to trip?

just stumbled onto this site and crossing my fingers that someone will be able to help. My problem is the tripping of an AFCI every 3/5 weeks when a 2nd TV is turned on. Sometimes soon afterwards, ...
6
votes
1answer
5k views

Why did my electric range wiring burn out at the terminal block?

Turned on our 2 year old stove (Whirlpool Gold) and heard fizzing noises, then smelled electrical burning. Went downstairs and shut off the breaker (40 amp). That was the only way to get it to stop ...
0
votes
1answer
47 views

Can you wire a 30A 2P standard circuit breaker “downstream” from a 60A GFCI 2p circuit breaker?

Will this still provide GFCI protection? Is this against code? Does this represent a hazard? I have a subpanel with a 60A GFCI circuit breaker, that I want to use that to feed to 2 30a 240v ...
2
votes
0answers
174 views

How do I troubleshoot a newly installed non-working outlet?

I recently spent several frustrating hours trying to figure out why an outlet on a new branch circuit would not power a load even though there was proper polarity at the outlet, my non-contact voltage ...
0
votes
2answers
122 views

Use of combination CAFCI and GFCI breakers instead of recepticles

I am about to begin a project that will include one or two new circuit for outdoor lights and receptacles attached to the main building. I will probably installing a new home run line from the panel ...
1
vote
2answers
60 views

Can I replace the main breaker in an electrical panel with a smaller one?

I have an older 60amp fuse box in a rental property that is wired as a sub panel off my main 100amp service. I would like to upgrade to a new circuit breaker panel so tenants can not pull out the ...
2
votes
3answers
4k views

Why does the circuit breaker for my bedroom continue to trip without any visible event after a power loss?

The 20A breaker for my bedroom will trip whenever we have a power outage at my house. If you reset it, it will trip again after an interval, say 5~10 seconds. The longer you wait to reset it, the ...
2
votes
4answers
63 views

Breakers tripping

USA (California) home with 240V 150A service. I have a contractor working on the house siding. He accidentally drilled though NM-B/Romex on a 15A circuit. (The repair of this is not my question and I ...
3
votes
1answer
109 views

When replacing non-grounding type receptacles is a GFCI receptacle required, or can any GFCI device be used?

Under the NEC (it was 210(7)(d)(3), but appears to have moved around some), it is permissible to replace an ungrounded receptacle with a GFCI receptacle, then wire further ungrounded or non-grounded ...
0
votes
1answer
52 views

Can I install tandem breakers in this panel, and would one 20 ampere circuit be enough for a garage?

I'm a home owner searching for information before hiring an electrician to come and do work on my home. What I want: Have a separate breaker\s to service a single car garage. 3 receptacles each ...
6
votes
2answers
701 views

How do I run a 3 Phase/1hp TEFC motor off of a regular household outlet?

I recently bought a brand new TECO-Westinghouse Electric motor . 3 phase HP: 1 Volts : 208-230/460 RPM: 1750 HZ: 60 Fr: 56 Cat no: ZA.0014TE2/56 Type : AEFAZA Enclosure : TEFC I would like to run ...
2
votes
3answers
185 views

Do receptacles require a 20 ampere breaker?

I thought wall recepticles required a 20 amp breaker. Am I wrong?
1
vote
1answer
59 views

Can I add a 50 amp breaker for an arc welder?

If my service disconnect breaker is a 150 and my fuse box isn't maxed out, 3 slots still available would I be pushing the limits to add a 50 amp breaker for a arc welder? I haven't pulled the cover ...
3
votes
5answers
155 views

Is this too many items on a 20 AMP Breaker?

I live in a 2 bedroom 2 bath duplex, where we have issue's with the light's flickering, often causing mini power surges, and at times kicking a breaker. One 20 ampere circuit supplies 3 ...
4
votes
5answers
316 views

How would I wire a thermal circuit breaker and switch together?

I want to wire a circuit breaker and switch to a GFCI and some other outlets. This is for power outlets on a work bench. Something like: I have this for a circuit breaker: and this for a switch: ...
1
vote
4answers
102 views

How many lights can be on one breaker?

How many lights can be run from one breaker I would like to add two two tube fluorescent lights to a string of lights I have already.
0
votes
0answers
31 views

No power to lights or receptacles yet meter shows 120 volts at breaker - 2 separate wires

Outlets and lights are not working from 2 separate wires coming out of my breaker box. Both main wires coming into the box show 120 volts each and the 15 amp breakers read 120 volts where the wires ...
3
votes
3answers
270 views

Why would a circuit breaker not trip if I accidentally shorted hot to neutral?

I am installing a set of recessed lights in a closet, replacing the existing fixtures one at a time. I removed power to the lights while installing each one by using the light switch, not the circuit ...
2
votes
2answers
55 views

Testing circuit breakers?

I have a panel of type XO circuit breakers in my house. One of them has failed closed (!) and I need to replace it. However, a few minutes on Google seems to indicate that this type of breaker is no ...
1
vote
1answer
57 views

GE Load Center Q's

I have an old GE meter socket load center (see picture). I have no idea what the model number is because the paper label on the inside of the lid is unreadable, and I have been unable to find any ...
1
vote
2answers
69 views

How do I go about determining how to wire a breaker box in a cargo trailer

I'm about to wire a cargo trailer with construction equipment, table saw, miter saw, air compressor, drill press, and a few other small tools. Only one tool and lights will used at one time. So here ...
2
votes
1answer
39 views

Should I replace an old breaker or add a new one?

Our old circuit breaker for our water heater seems to be at the end of its life. However, the breaker also controls our well system, and the breaker is only 20 amps. Is it okay for us to just replace ...
2
votes
1answer
78 views

20amp breaker trips with NO load…Continuity between black & white wire at electrical box

I have a 20 amp breaker that connects to one wall in my kitchen. It operates 3 outlets, a microwave and two other outlets used for a toaster oven & the last a blender. On the blender outlet ...
0
votes
0answers
46 views

Single pole circuit breaker won't close unless double pole above it is closed

I was trying to find out where a trip was in my house and turned off a double-pole breaker then a single-pole breaker. Went in reverse order to turn single-pole back on and it would trip back open ...
0
votes
3answers
156 views

Three dead power outlets, no tripped breakers

A few days ago I was using a multimeter to check for current to the thermostat on my garage refrigerator. I wasn't thinking and did something wrong (wrong HOT, I believe) and power to the refrigerator ...
2
votes
2answers
120 views

What size replacement fuse is required for this hot tub?

I recently had a power outage that blew one of our air conditioning fuses (which we were able to fix) and one of the fuses (out of two) in our spa equipment service control board. Next to both fuse ...
2
votes
2answers
118 views

What's the amperage on a circuit breaker that's “linked” together?

On our circuit breaker, we have several circuits that are linked together by a metal handle. For instance, there are several cases of three 20A circuits all linked together, meaning you can only flip ...
1
vote
2answers
92 views

Why use AFCI receptacles rather than AFCI breakers?

Is there any reason to use an AFCI receptacle rather than replacing the breaker with an AFCI type? It seems that providing protection on the whole circuit makes much more sense than to just one ...
3
votes
2answers
81 views

How to fix double-tapped 14-3 cable to boiler

I have an oil boiler for heat. 14-3 cable runs from the panel to a thermal cutoff above the boiler, then into the boiler's control box, and from there to a Taco controller that manages three zone ...
0
votes
0answers
126 views

Why is my bathroom vent fan tripping the GFCI when being shut off?

I have a GFCI tripping when a vent fan is being shut off. I saw in KeithS's answer to a similar question that the blades rotating after shut off causes an imbalance, tripping the GFCI. In my case the ...
1
vote
0answers
58 views

How to know that new appliance won't trip the circuit?

I'm buying new appliances and want to make sure I won't trip the circuit. MW/convection is 950 W, 1750 W and 900W for three different functions. There is 20 Amp circuit for that. the new stove ...
0
votes
1answer
624 views

Can you put a small breaker panel after a 30 amp breaker from main panel in the house?

Looking to run lights in my garage. If I put a 30 amp breaker in my main panel on a 10 wire to a small breaker panel in my garage, can I put 2-4 15 amp breakers out there for the lights? Likewise, ...
0
votes
2answers
130 views

Lights and outlets on multiple circuits out but no circuits tripped. Power back to normal after several hours

for the past several days the lights and outlets to multiple rooms in my house have been going out, yet no circuits are tripped. This is happening to lights and outlets on multiple circuits. The weird ...
2
votes
3answers
946 views

can you combine 2 circuits into 1?

Can I safely combine two 15 amp double pole circuits into a single 30 amp double pole circuit? I am trying to make space in my 200 amp box to put a 40 amp double pole breaker to support a water ...
1
vote
2answers
516 views

How do i know if my service panel will accommodate a 240v circuit breaker

We are looking to install a hot tub and trying to find out if our service panel will accommodate a 240v circuit breaker. This is what our panel says but I do not know what all of this means: ...
0
votes
1answer
103 views

Is 40-amp breaker enough for my new range?

My new range says it needs a 40-amp circuit breaker minimum. But it also says maximum draw is 13,200 watts on 120/240, so doesn't that mean a 40-amp breaker would be inadequate? By my math, max ...
2
votes
2answers
2k views

How do I connect a timer to circuit box which controls our outside lights?

Currently our outdoor lights are being controlled by the circuit breaker in the box. We want to connect a timer to the circuit-breaker. There is a junction box with Black, White and a bare ground ...
1
vote
1answer
331 views

What to look at first when when circut breaker that fridge is on is tripping?

I have a house where the circuit breaker has tripped a few time over the last several days. It flipped one evening, we flipped it back and was ok for a couple days. We went away for the weekend and ...
3
votes
3answers
111 views

Why am I getting no power to the branch circuits with a new sub-panel?

My home had an ancient Zinsco sub-panel in which the breakers were grounding out and arcing to the panel. I've swapped it with a new Eaton 100 amp panel. I've re-installed all the breakers, and ...
2
votes
4answers
12k views

Why does the main circuit breaker trip but not the smaller branch circuit breakers?

We have one circuit breaker (40 ampere) in entry point of electricity line in our house, than we divided it into two separate line in two levels and put one circuit breaker( 32 ampere) in level one ...
2
votes
2answers
91 views

Curcuit breaker not accesible

My dryer stopped working and I found out that the circuit breaker (fuse) had burnt out. I measured the voltage in the socket and it's none. I live in an older house in USA and the cable is inside the ...
5
votes
3answers
4k views

Does turning circuit breakers off cause wear?

A comment over on another SE got me thinking. With screw-in fuses, unscrewing it and then later screwing it back in causes negligible wear on either part of the installation. But what about modern ...
2
votes
3answers
367 views

Any problem with installing two identical circuit breakers in series?

Suppose I want to reduce risk of a circuit breaker malfunctioning and failing to disconnect a shorted circuit. What if I install two identical breakers sequentially (one after another) so that if one ...
2
votes
1answer
79 views

Main breaker on load center won't open

I was in the process of connecting a Reliance generator trow over switch , although the job was completed , I was trying to shut off power to the entire house by opening the main breaker but would not ...
0
votes
1answer
289 views

What subpanel and number of circuit breakers should I install in a detached garage?

I no longer am dealing with my contractor. Long story. But he ran 2 10-3 wires out to my garage for power. I think he was planning on putting a 30 amp breaker on the panel in the house for each wire ...
2
votes
1answer
81 views

Is my water heater connected to GFCI and is it affected after short circuit?

I am an absolute n00b when it comes to home electrical systems. Please do forgive me if this is a repeat question since I wouldn't know what to search for. I am in France and I have 230V supply at ...
7
votes
1answer
34k views

Why is my air conditioner tripping the circuit breaker?

Our air conditioner recently stopped blowing out cold air. When I went to check on it, I noticed that the outside unit wasn't coming on. We had had problems with ants in the contacter in the past, ...