I have a 3 wire outlet with the entrances for hot, neutral and ground. But I know that the ground entrance is not really grounded, so in effect useless. Now, since the neutral is grounded, could I connect the ground entrance with the neutral therefore grounding the ground? What would be the problem with that?
I don't believe this is up to code, but it will pass the test from a standard outlet tester. The problem I see is if any device plugged into the outlet comes into contact with a ground (e.g. water) and that path is more efficient than going all the way back on the neutral wire through the house wiring, then hot current going through any appliance and onto the neutral would come out the ground and possibly electrocute anyone in that path. That said, I've seen this implemented and have lived in a home where this was done without dying, or even getting shocked. But the fact that the electrician that used this trick was missing several fingers should give you pause. |
I'm not in the US. Where I live this (called "combined neutral and protective earth wire") is only allowed in non-domestic power distribution. This setup has one major problem: if phase and neutral are swapped (for example, you alter wiring in the box next to the power meter and swap wires) phase is now supplied onto the grounding contact as well and that's asking for trouble. So you can try do that, it's likely better than no grounding, but it's likely not up to code, and it is hazardous in that if wiring is altered you can have phase on the grounding contact and hence on appliance case. |
The ground is supposed to provide an alternate path to ground, in case the neutral wire doesn't do a good enough job. I don't know of any cases where the neutral would be compromised while a ground wire in the same sheath isn't -- except where someone mucked with the wiring. If you only have two wires, that tells me you're in an older house. So it's possible (likely!) that a former homeowner did something wrong, like put a switch in the neutral, or reversed polarity. If you know all of the devices on a particular circuit, you can do the detective work to ensure that this hasn't happened. Or you can run a separate ground wire to a water pipe. This does meet code in the US (at least as-of 1999, which is what my electrical handbook is based on), and it's what I did for my home office (I wasn't happy having computers on ungrounded circuits). To completely meet code, you need to ensure that the cold water pipe has a conductive strap to bypass the water meter. And you need to use a wire that is the same gauge as that used for the circuit (14ga for a 15 amp circuit). |
nuetral should be connected to ground so that any appliances touch the hot wire you will not be electricuted because even one hot wire touch any appliances and your stepping on the ground or holding any metal and touch that appliances you will be electricuted and that metal your touching will serves as ground. |
There is no such thing as neutral in electricity. That would mean not being used. the neutral and ground are both ground paths. The issue is that the ground wire is usually used to dissipate static. while it should work and cause no problems I would not want to trust it with a pc or power tool. Both wires run to the exact same bars on a breaker box so in theory itll be ok but now you'd be trying to get rid of static down a line trying to deal with power from the supply side. |