Take the 2-minute tour ×
Home Improvement Stack Exchange is a question and answer site for contractors and serious DIYers. It's 100% free, no registration required.

I'm looking to wire up the second floor of my house and the cold air return provides a convenient, straight run from the office to the utility room. Is it safe and within code to run ethernet cable in the air return?

The air returns are not metal ducts, they are just open cavities in the studs.

Scope of this question is purely limited to running network cable through an air return, decisions on wired/wireless and the various wired options have already been made.

share|improve this question
2  
Why not just use wireless? –  user558 Sep 11 '11 at 12:43
3  
Are your air returns to code?!?! –  Loren Pechtel Sep 11 '11 at 21:39
    
If wireless isn't an option, why not use powerline networking? –  Mike B Sep 11 '11 at 22:45
2  
@freiheit It appears I gave you some bad advice before, please see my updated answer for more accurate information. –  Tester101 Mar 4 '13 at 15:59

3 Answers 3

up vote 10 down vote accepted

National Electrical Code 2008

300.22 Wiring in Ducts, Plenums, and Other Air-Handling Spaces.
(B) Ducts or Plenums Used for Environmental Air. Only wiring methods consisting of Type MI cable, Type MC cable employing a smooth or corrugated impervious metal sheath without an overall nonmetallic covering, electrical metallic tubing, flexible metallic tubing, intermediate metal conduit, or rigid metal conduit without an overall nonmetallic covering shall be installed in ducts or plenums specifically fabricated to transport environmental air. Flexible metal conduit shall be permitted, in lengths not to exceed 1.2 m (4 ft), to connect physically adjustable equipment and devices permitted to be in these ducts and plenum chambers. The connectors used with flexible metal conduit shall effectively close any openings in the connection. Equipment and devices shall be permitted within such ducts or plenum chambers only if necessary for their direct action upon, or sensing of, the contained air. Where equipment or devices are installed and illumination is necessary to facilitate maintenance and repair, enclosed gasketed-type luminaires shall be permitted.

Which means, NO. The only wiring allowed in ducts, is wiring that is "necessary for their direct action upon, or sensing of, the contained air.".

Mike Holt explains it well in this YouTube video.

If you read article 725, you'll see that it references back to section 300.22.

share|improve this answer
    
Thanks, my area has only adopted NEC 2008, and as I'm not an electrician, I don't follow much besides what is currently allowed in my area. –  Karl Katzke Sep 13 '11 at 17:31
1  
The paragraph does not say that the only purpose of the wires must be connected to the sensing of the contained air. Therefore, if the network has such a monitoring function (controlled by some application that runs on a server) and it happens to serve media at the same time, multiplexed in the same data stream over the same physical wire, the requirement is met. –  Kaz Mar 5 '13 at 8:04
1  
@Kaz You can try it, but I'm betting the inspector says no. –  Tester101 Mar 5 '13 at 13:07

Looking in 2011 National Electric Code Changes of Interest, they reference NFPA 90A-2009 :

Section 4.3.4 of NFPA 90A-2009 states that “Wiring shall not be installed in air ducts” unless it is “directly associated with the air distribution system and does not exceed 1.22m (4 ft).”

I don't have access to the full code, but just in the notes on the revisions to NEC 2011, they seem to allow CMP (plenum rated cable) in air ducts or "other spaces used for environmental air" based on the table on page 15, 'Applications of Communications Wires and Cables'. All others must be in a raceway ... other than CMUC (under carpet) or cables w/ power, which are both banned completely.

I'd personally ask a local inspector -- they're the ones who are going to know what the local interpretation of the codes are. If you're running something that's not required to be inspected, I'd only run plenum rated cable -- the jacket won't give off toxic fumes if burned, so you'll have a chance at escaping a fire without being poisoned first.

share|improve this answer

Yes, it is within code to run a low voltage wire inside an air return (aka plenum) in the US. You'll even find cable that is "plenum rated" -- which means it has a lighter jacket on it -- that is specifically meant for use in plenums where it's less likely to encounter sharp edges or be overly stretched during pulls. (I'd still use normal cable, though, because pulling plenum cable, even through a plenum, is difficult unless you pull it in a large bundle with proper knowledge.)

Source: NEC 2008: Chapter 7, Article 725

share|improve this answer
15  
Plenum cable is actually fire-retardant: it is made with a low-smoke polyvinyl chloride (PVC) or a fluorinated ethylene polymer (FEP). It's stiffer and a bit more brittle than riser cable (which has lower fire ratings, but is rated to travel between floors), which is again is a bit more brittle than patch cable. Patch cable is not rated for use in walls, it's the one you see on patch panels or from the wall to your PC/whatever. –  gregmac Sep 11 '11 at 21:33
    
Can you cite the code section? –  Freiheit Sep 12 '11 at 13:49
4  
NEC 2008: Chapter 7, Article 725 –  Karl Katzke Sep 12 '11 at 14:55
1  
Article 725 references section 300.22, which says no wires in ducts. –  Tester101 Mar 4 '13 at 15:57

Your Answer

 
discard

By posting your answer, you agree to the privacy policy and terms of service.

Not the answer you're looking for? Browse other questions tagged or ask your own question.