Tell me more ×
Home Improvement Stack Exchange is a question and answer site for contractors and serious DIYers. It's 100% free, no registration required.

My vegetable sprayer line broke yesterday, which led me underneath my sink. It wasn't until I was kneeling in a large puddle of water with the line draining on me and the floor that I realized how bad the wiring was for my garbage disposal:

Shocking finding under my sink

This obviously needs to be addressed. My question is which of the following approaches will solve my problem and won't kill the next tenant?

  • Cover the J-box with a plate that has a hole and let the romex come through
  • Wire in an outlet (half-hot) and convert the romex to a 3-prong plug
  • Wire in a GFCI outlet (half-hot) and convert the romex to a 3-prong plug
  • Something else?

Completed project:

All tidied up, likely not to kill me

share|improve this question
Do you know if that circuit already has a GFCI on it? – Niall C. Jul 29 '11 at 15:26
The breaker box has a "GFCI protected" sticker on the label panel...but I've yet to find said outlet. – sixlettervariables Jul 29 '11 at 15:32
1  
That's odd; there are GFCI circuit breakers, but the protection is actually better (and cheaper) at the outlet itself. See if there's a three-prong outlet on the same circuit, and plug in an outlet tester with a GFCI test button to verify the disposal will cut out with a ground fault. – KeithS Jul 29 '11 at 16:26
There are no GFCI outlets on the circuit as far as I can tell. – sixlettervariables Jul 29 '11 at 16:34

3 Answers

up vote 4 down vote accepted

The answer to your question depends completely on whether this node in the circuit is GFCI-protected. GFCI protection is an absolute must for your disposer; it's a high-amperage electric motor hooked up to your kitchen drain.

Since this J-box doesn't have a standard 3-prong outlet, you'll need to find another outlet on the same circuit; look for a countertop outlet nearby. Plug in an outlet tester (like the one below, available for $5-10 from your local big-box home improvement store), turn on the disposer, and hit the black button on the tester to short hot to ground, inducing a "ground fault".

enter image description here

If the disposer has GFCI protection, it will cut out, and you're golden as far as circuit safety. If not, you definitely need to rewire this J-box with a GFCI outlet.

Even if the disposer is GFCI protected, you have other problems. The outlet is in a "wet" place; you hope that the under-sink area never leaks, but there is always, always, a plumbing emergency at the kitchen sink at some point. To avoid a continuous ground fault through contact with standing water in the J-box (which would prevent you from resetting the GFCI until the whole area dried out), you should seal this area as best you can. A little adhesive spray foam to fill the gap between the wall and the back of the cabinet, followed by a layer of silicone adhesive caulk to waterproof the spray foam (people think spray foam is waterproof, but it really isn't), and a child-resistant outlet and plate with a rubber or neoprene gasket (and/or another dab of silicone) should keep the water out in any situation less than a full flood.

share|improve this answer
Excellent, I have an outlet tester but it does not come with GFCI testing. If it's GFCI protected, would it be worth wiring in a normal outlet half-hot (top switched, bottom hot) and switching the disposal to a cord? – sixlettervariables Jul 29 '11 at 16:48
2  
IMO, yes. Any licensed electrician will look at the hack-job that was done to this setup and insist that it be properly terminated in an outlet and plated. Depending on local code he may also require some sort of water seal to keep drips and sprays out of the J-box. Since this is apparently your own house, you can get away with just plating over the wire-nutted connection in terms of it working and not being a total shock hazard, but as a proud homeowner if this were my house I'd do the job right. – KeithS Jul 29 '11 at 16:55
It's my landlord's place, but he works with me on rent if I fix problems (I've already replaced a good number of outlets/switches that were fire hazards). Game plan is outlet, switch to cord, weatherproof plate. – sixlettervariables Jul 29 '11 at 17:07
The disposal should not be connected to the countertop "appliance" receptacles, it's likely the disposal is on it's own branch circuit. – Tester101 Jul 29 '11 at 17:30
Depends on the age of the house; it's been perfectly acceptable for a long time. In my house built in '80, a countertop outlet, the disposer and an outlet on the island are on one circuit, then the fridge, microwave and the second countertop outlet are on another circuit. No problems electrically (though I did have to make sure the fridge and microwave outlets weren't GFCI protected along with the countertop), until you start mixing in arc fault circuit breakers, at which point the big electric motor may need a non-AFCI breaker when ordinary outlets require an AFCI by current code. – KeithS Jul 29 '11 at 17:36
show 7 more comments

If you don't have the GFCI tester that KeithS mentioned, they are cheap and good to have. But until then, just hit the test button on the GFCI outlet in the kitchen and see what turns off.

As far as wiring coming straight out of the box like that, I suspect it's against code. Every wire should go through a knockout in the back of the outlet in a secure way, either using the plastic tabs or a securely screwed knockout clamp:

wire clamp

With the current setup, there's a risk of pulling on the wires and loosening the connection. Even putting a blank plate with the wire coming through doesn't secure the cable and connections. But as the fellow DIYers below point out, you can get a box cover with a knockout and use that to clamp the wire in (and also shield it from some water or physical contact):

box cover with knockout

share|improve this answer
What about a Box cover with a knockout? – Tester101 Jul 29 '11 at 18:30
1  
Are there any code issues with a "plugged in" disposal? – Tester101 Jul 29 '11 at 18:35
Something like this plastic cover w/ screwouts? – sixlettervariables Jul 29 '11 at 18:45
I actually went searching for a box cover with a knockout, but with slightly different terms, and didn't see it. Thanks guys! – BMitch Jul 29 '11 at 20:22
@Tester101, great question. Don't know of any myself, but perhaps Sherlock will chime in. – BMitch Jul 29 '11 at 20:27
show 1 more comment

Pretty good advice so far.

If it were a new install, then it would not be "J" boxed under the sink, but direct to the switch and GFI protected.

But with the situation you have now, unless you want to fish wires up the wall to the switch, let's make it safe.

  1. Install a tamper proof GFI receptacle into the box as pictured and install a gasketed cover.

  2. Install a 3 prong plug to the cord from the disposal. It should be a 3 wire cord if made or installed in the last 20 years. You can also find plugs with a rubber bushing that will fit snug around the existing cord. If it is not 3 wire, open the hatch on the disposer and install a new 3 wire piece of SO or SJTO cord with a molded plug already attached.

Even if the circuit is already GFI protected, a second GFI at the point of power will not hurt, and give you more protection in a future geyser blast!

All this is assuming that the feed romex is actually a true 3 wire circuit, hot, neutral, ground.

share|improve this answer
Fixed up the formatting of the post; hope you like it. – Jay Bazuzi Jul 29 '11 at 21:12
@sixlettervariables: It can be difficult to make sure that the 3 wires are correct as shirlockhomes specifies. Specifically if neutral and ground are not separate conductors all the way back to the main panel, a plug tester won't tell you that. – Jay Bazuzi Jul 29 '11 at 21:15
+1 for "giving it a shot" :) I like to take a step back to the pros my lack of knowledge on the NEC risks giving bad advice. – BMitch Jul 29 '11 at 21:42
2  
Don't forget the drip loop. You don't want water running down the cord and into the receptacle. This article has a good explanation (it's talking about one for an aquarium, but the same principle applies). – Tester101 Jul 29 '11 at 21:54
Thanks for the edit Jay. Looks much better. – shirlock homes Jul 29 '11 at 22:11
show 3 more comments

Your Answer

 
discard

By posting your answer, you agree to the privacy policy and terms of service.

Not the answer you're looking for? Browse other questions tagged or ask your own question.