I'm working on a small cabin. All black wires are run directly to lights. The white wires are run to the switches then lights... so each switch has only white wires.

Would the circuit still work? Why or why not?

5
  • 2
    Can you provide pictures? This sounds really unconventional and probably completely non code-compliant. Commented Aug 4, 2015 at 23:04
  • 2
    Could you provide a sketch or diagram explaining exactly what you mean? It sounds like you're talking about switching the grounded (neutral), but it's hard to tell if that's what you mean.
    – Tester101
    Commented Aug 4, 2015 at 23:06
  • 1
    Is it safe to assume you're in North America somewhere? Are these lights AC (from a utility, a generator or from an inverter), or DC from a battery bank? Commented Aug 4, 2015 at 23:07
  • 2
    Yeah, who built this cabin and when? And is this AC or DC power? Commented Aug 4, 2015 at 23:53
  • This same question was asked again here: Hooking up switches only with white wires. Will it work? Commented Aug 9, 2015 at 20:51

2 Answers 2

3

Aside from being a code violation of outrageous proportions, if this is 120VAC you would have the delightful condition that the light sockets were always hot/live - this can make changing a lightbulb into a shocking experience, and under the right conditions, also your last.

You may also get some interesting magnetic effects from the loop wiring.

Don't do this. The only level it "works" at is the Dr. Frankenstein's Laboratory level, and most people are not as tough as Igor. If it's actually something you found (or even, nay, especially, if it's something you are responsible for creating), rip it the heck out and do it right.

2
  • Don't hold back, Ecnerwal, tell us how you really feel... ;-) Commented Aug 5, 2015 at 1:22
  • @Craig Hurr! Arggh! Urrgh!
    – Ecnerwal
    Commented Aug 5, 2015 at 1:28
1

Maybe I'm answering too soon (hopefully you'll post a diagram and/or pictures). But offhand and assuming you're using 120V AC power, this doesn't sound so good. Yes, there's a fair chance that you could make it function, but probably not really in compliance with the rules. It sounds like at best you're switching on the neutrals, but it's hard to tell without more details.

I presume the cabin is supplied with 120V AC circuits? If this is actually 12V DC, you're going to be surprised at how big the wires need to be. You probably won't be happy with lighting over smaller than #10 wires because you get rapid voltage drop over short distances with low voltage, and smaller wires result in even more voltage drop. But with 12V low voltage circuits you also won't have the same code requirements as for 120/240V AC.

Assuming you're wiring for AC

If you have single wires running independently to the light fixtures and the switches, you're not in code compliance (for residential AC service) even if the wires are in conduit (the wires for a circuit need to run together, so you can't run the "hot" and "neutral" along different routes). For a circuit to actually function, you need a supply conductor (the "hot," typically black) and a return conductor (the "neutral," typically white), and the electrical code requires a grounding conductor for anything new or anything you make substantial changes to.

If you were using standard 14/2 or 12/2 NM cable, you would have a black ("hot"), white ("neutral") and a bare grounding wire in each cable.

So you would have at least a black and a white conductor in each light fixture and in the switch box(es).

You'd have a supply cable feeding power into either the switch box or your light fixture(s). If power feeds into the light fixture, you'd have a switch loop to the switch box, which you would use 14/3 or 12/3 cable for (black, red and white plus a bare ground wire). That way you can provide a neutral in the switch box as required by current code and use the black and red for the switch loop for the supply side.

13
  • My parent's old RV is wired with what seems to be around #14 stranded wire on the DC circuits and the incandescents are fairly bright - #14 will carry 10A at some moderate voltage drop (30 ft for a 5% drop), still providing around 100+ watts of power at the other end.
    – Johnny
    Commented Aug 4, 2015 at 23:45
  • ...but if you're going to wire up something like a few CFL's that will make a room or two in a cabin moderately bright... just saying. ;-) Commented Aug 4, 2015 at 23:50
  • Also, part of what's going on with that 5% drop over 30 feet is that you're running your battery down faster without realizing any benefit from the extra energy expenditure. But of course it's a balancing act. Commented Aug 4, 2015 at 23:52
  • Yeah, but a couple 30W 12V Fluorescents doesn't need 10 gauge wire (and the installer/manufacturer isn't going to use 10 gauge unless he has to). Losing 5% to wiring loss doesn't sound that bad, even the NEC allows for a 5% voltage drop on branch circuits. A couple 30W fluorescents will do a decent job of illuminating a small cabin or large RV - you might not be reading a book under that light, but you can at least see where you're going)
    – Johnny
    Commented Aug 5, 2015 at 1:03
  • @Johnny Have you ever really tried to read by the light of a single 30W CFL? ;-) The NEC allows for 5% voltage drop on AC branch circuits, but they're not taking into consideration trying to make a measly car battery (or deep cycle marine battery) run your lights for that all-important extra 20 minutes, either. ;-) Commented Aug 5, 2015 at 1:08