Home Improvement Stack Exchange is a question and answer site for contractors and serious DIYers. It's 100% free, no registration required.

Sign up
Here's how it works:
  1. Anybody can ask a question
  2. Anybody can answer
  3. The best answers are voted up and rise to the top

I installed a new dryer in our house. It runs but won't heat. It has a 240V 3 wire connection. There is a 30 amp double pole breaker installed in the breaker box. (the box is very old) I've read that you should get 120V from each leg to the neutral which I do. I also read that you should get 240V across the two. Only a few volts register on the meter, not 240. How is this possible and what changes should I make to correct this?

share|improve this question
    
Where are you taking the measurement at the breaker box, or at the receptacle? – Tester101 May 7 '11 at 14:09
    
Please measure the voltage at the breaker and let us know what you get. Who installed the breaker? Has it been successfully used before? – Philip Ngai Apr 25 '12 at 22:04

Look at the vertical location of your double pole breaker. The first 2 slots in a column are on one phase, the next two are on the other phase. A double pole breaker has to have one connection to each phase, so it has to start on an even location. Look at the breaker for the stove, your dryer needs to be an even number of locations away from it.

share|improve this answer
2  
This is incorrect: every other position is a different phase. A 240V breaker always spans two phases, it doesn't matter where it is. – gregmac May 11 '11 at 1:27

Is it possible that both poles are connected to the same phase (e.g., if your house only has 120-volt service)?

share|improve this answer
    
I was taking the measurement at the recepticle. There are a couple other 2 pole breakers and I'm pretty sure that the oven is 240V. Could a section of the breaker box be only 120V and another 240V. This is an old breaker box so I'm not sure. – Jon May 7 '11 at 16:28

Your Answer

 
discard

By posting your answer, you agree to the privacy policy and terms of service.

Not the answer you're looking for? Browse other questions tagged or ask your own question.