I am replacing all my electicial outlets and only one has wires that are too big to put into the back of the new outlet. Any suggestions?
|
|
As long as you are going through the trouble to replace your receptacles, I have some recommendations:
As others have noted, it sounds like you're trying to insert 12ga wire in to a hole that only fits 14ga (for a 15A circuit). Don't use that feature; see #3. |
|||
|
|
You probably have 12 gauge wire on that part of the circuit, which won't fit into the push-in connector on the back of a 15A receptacle (it's only good for 14 gauge). Is that the only receptacle on that branch circuit? If so, it might be a 20A circuit, so you'd need a 20A receptacle (otherwise you risk overloading the receptacle and damaging it, which could lead to a fire):
But as @DA01 says in his comment above, always use the screw terminals. They give a much more secure connection. |
|||||||||
|