Home Improvement Stack Exchange is a question and answer site for contractors and serious DIYers. It's 100% free, no registration required.

Sign up
Here's how it works:
  1. Anybody can ask a question
  2. Anybody can answer
  3. The best answers are voted up and rise to the top

If stranded wire can carry more power for a given wire gauge, why are homes typically wired using solid?

If solid wire is less expensive to make, that provides a compelling reason why solid is used, but if an electrician or homeowner wanted to use stranded, is there any reason not to?

For this question I am mainly referring to legs of U.S. home wiring for 15 and 20 amp breakers carrying 120 volts on a single phase.

share|improve this question
up vote 17 down vote accepted

A few reasons:

  • Stranded wire is more expensive to make.
  • At a given wire gauge, stranded is going to be larger than solid wire (it's the cross-sectional area of conductor that counts and there are going to be some air gaps between conductors with stranded). This could make a big difference if you have several cables in a limited space like an electrical box.
  • The main advantage of stranded is that it's more flexible. You generally don't need this in home wiring because it's all put in place once and hidden behind walls/floors/ceilings.
  • When you screw a solid wire into a switch or receptacle, you can tell if it's secure. I could see individual strands coming loose as you fold wires back into an electrical box.

More information in Wikipedia: http://en.wikipedia.org/wiki/Wire#Solid_versus_stranded

share|improve this answer
1  
Somehow, I started with your Wikipedia link and ended up here. Randall Munroe was right! – Doresoom Apr 26 '11 at 21:30
    
Once you get upto 6mm, then you do need stranded to get enough flex, but I agree with you list for lower rated cables – Walker Nov 16 '11 at 14:21
    
In addition to this, solid is just nicer to splice together with a wire-nut: it's easier to line the two wires up, they don't tear if you pull on them too hard when checking the connection, and they don't get all frizzy and break apart if you have to undo the wire-nut. – BlueRaja - Danny Pflughoeft Sep 7 '13 at 7:02

The skin depth for copper wires is roughly 1/3" for 60 Hz. So unless your wire is more than 2/3" in diameter (YIKES!), it won't come into play.

Therefore, solid copper wire CAN carry more power than stranded wire at 60 Hz, due to packing inefficiencies (empty space) that is inevitably between the individual strands.

share|improve this answer

Stranded is more susceptible to corrosion due to more surface area.

share|improve this answer

We're looking for long answers that provide some explanation and context. Don't just give a one-line answer; explain why your answer is right, ideally with citations. Answers that don't include explanations may be removed.

For AC - electrons run through entire cross-section the of wire

For DC - electrons like to run on the outside of the wire so stranded will have more surface area for a given gauge

share|improve this answer
6  
You have this backwards; see the skin effect. – JYelton Feb 21 '14 at 16:59

protected by Steven Aug 19 '15 at 14:47

Thank you for your interest in this question. Because it has attracted low-quality or spam answers that had to be removed, posting an answer now requires 10 reputation on this site (the association bonus does not count).

Would you like to answer one of these unanswered questions instead?

Not the answer you're looking for? Browse other questions tagged or ask your own question.