I've really got two possibly related issues here. We have a basement office that we wired ourselves. Code required that we put in an AFCI breaker. From what I've read these can be pretty temperamental and that has been the case with us. The breaker will trip as often as once a day but it is usually less often. We replaced the original AFCI breaker and for about a month after we were good. However, now it has started tripping often again.

I have a surge protector hooked up on one outlet with a PC and monitor attached. It is the kind of surge protector with the master outlet that can control the other devices so they turn on/off when the master device turns on/off. I've noticed that anytime we run the garbage disposal upstairs and also at many random times throughout the day, the surge protector will make a clicking sound, like the power has come on/gone off of the main device (the PC). The PC isn't turned on.

Any ideas what might be going on here, both with the breaker flipping and/or the surge protector clicking? I know we have mixed wiring of 15A (14 gauge, white) and 20A (12 gauge, yellow). The AFCI breaker itself is 15A. Could either of those be a possible problem or does it sound like this is something else? Bad outlet(s) along the circuit?

share|improve this question
    
Is the office the only thing on the circuit, or does the circuit supply other rooms too? –  Tester101 Mar 15 '11 at 12:28
    
Are there any GFCI receptacles on the circuit? –  Tester101 Mar 15 '11 at 16:49
    
The office does have one wall shared with our family room that has the TV, DVR, and a computer plugged in. There are no GFCIs on the circuit. –  Jeremy Hicks Mar 15 '11 at 18:44
    
How many fixtures (receptacles, lights) are on the circuit? Are unusual items plugged in / running when it trips (vacuum cleaner, circular saw, one particular lamp)? –  Tester101 Mar 15 '11 at 19:57
    
I'm not sure how many are exactly on the circuit. I made sure to keep it under 10 per circuit. Nothing unusual plugged in when it trips. Usually it is when I'm on the computer. It has happened with a couple of different computers. It has only happened a couple of times when I was just watching TV. –  Jeremy Hicks Mar 16 '11 at 14:12
show 2 more comments

3 Answers

I've had some issues with AFICs in the past, and one quick thing you should check (which ended up being my problem): Is the insulation on the wire coming into the outlet box pinched and causing a loose/flaky connection? That will still give power to the outlet (under a normal breaker) and won't trip a normal breaker, but it'll drive an AFCI nuts.

Another technique you can try to debug this is by swapping in a GFCI breaker, and see if that trips too. If the GFCI trips, it's a grounding problem. If it only trips on the AFCI, then there's arcing somewhere along the circuit. Check junction boxes, the outlet boxes and the connections to the plugs in the boxes.

Happy & Safe Debugging!

share|improve this answer
    
Oddly enough, my breaker hasn't tripped again since the day I posted my question here! Very strange. I looked up the manual for this particular breaker and it has an indicator light (when it trips) that tries to indicate what the real problem is - whether is it load related or an arc fault. However, I haven't been able to check since it hasn't tripped. Thanks for the tips. –  Jeremy Hicks May 16 '11 at 14:22
add comment

I wasn't sure what an AFCI was, so I did a quick google search. I came up with this page:

http://www.thecircuitdetective.com/afci_circuit_breakers.htm

which gives lots of info and a detailed procedure for troubleshooting this issue. In particular, it sounds to me like your issue might be the shared ground problem, ground from one circuit mistakenly connected to ground from another circuit. That said, the troubleshooting procedure is rather involved. See the page above, and then decide if you want to attack it yourself or call an electrician. Hope this helps.

share|improve this answer
2  
I think you mean a shared "neutral" problem. The ground should be common for all the circuits in the house. –  RSMoser Mar 15 '11 at 17:55
    
I have seen that circuit detective site and it did help a little. I also did a little more digging on our particular AFCI. It is Siemens brand and apparently has an indicator light to help diagnose what is causing the breaker to trip. If there is no light then it means either an overload or a short-circuit. If there is a light it means an arc fault or a ground fault. I'll post here next time it trips with the results. –  Jeremy Hicks Mar 15 '11 at 18:48
add comment

Your AFCI is behaving as it should.

That clicking you hear in your power strip is a relay clicking. A relay is a mechanical switch activated by a magnetic field. The act of opening an closing the switch will cause an arc. A tiny one, but still an arc. Opening and closing a bunch of times in a row means more arc.

You need to figure out why the power strip clicks. It might be sensitive to under-voltage, and when your disposal is running, it might lower the voltage in your entire house just a bit.

I suggest replacing your power strip with a band-new, no frills type and see if that solves your problem.

share|improve this answer
add comment