Home Improvement Stack Exchange is a question and answer site for contractors and serious DIYers. It's 100% free, no registration required.

Sign up
Here's how it works:
  1. Anybody can ask a question
  2. Anybody can answer
  3. The best answers are voted up and rise to the top

One of the double sockets in our garage needed replacing (damaged after a washing pole hit it) - a pretty trivial job that I'd done before. So I flipped the MCB for the ring main, used a non-contact voltage tester to check nothing was there, and set to work. I disconnected the old socket fine, and was lining the cables up to fit into the new socket when... ow.

My finger bridged the live and earth pins, and suffice to say the live wire was very much alive. Bar a few finger spasms I was fine fortunately, and believe me I realise I was very lucky in that respect (I'm in the UK, so that was 240V.) Before finishing the job I then shut off the entire property's electrics - I was taking no more chances.

Further inspection confirmed two things I immediately suspected at this point - the MCB in the garage (installed before we moved into the house) was shutting off power via the neutral, not the live, and the voltage tester was dodgy (I had tested it on the same socket earlier and it seemed fine, further testing showed it presumably had a loose connection internally and only worked sporadically.) Needless to say it's now in the bin, and an electrician has been called to sort the MCB and check the rest of the house for similar issues.

Unsurprisingly this has shaken me up a bit - I would say I'm a rather safety conscious person, and in this case thought I'd done all the checks properly (including taping over the relevant trip switch to ensure no-one flipped it back on while I was working.) In some ways I can't help feeling I was unlucky that the MCB was wired by a cowboy, in combination with the voltage tester failing in the way that it did, at the time that it did. However, I'm not one to solely blame tools - clearly some, if not most of the blame here lies with myself also.

So in short, what should I have done differently - and was I primarily being stupid, or really quite unlucky?

share|improve this question
6  
I have a habit that if I'm sure that something is not live and I'm about to touch it, then before that I connect the live&earth pins with whatever (insulated handle) tool I have in hand. It's quick enough to do it by habit even in cases where you wouldn't pull out a tester, but if you're about to make a mistake then it shows you that without risk of life. – Peteris Aug 17 '14 at 9:03
1  
If you read the directions that come with non-contact testers, it says to check it for proper operation on a live circuit. So what I do is push the button near a live circuit, and while holding it bring it to the circuit under test, then back to the live one. – Brad Gilbert Aug 17 '14 at 15:16
1  
#1 Rule: The wire is always live. – Phonics The Hedgehog Aug 18 '14 at 2:12
1  
I've been shocked too. All I was doing was taking the cord out of the socket so I could plug something else in but it was pretty difficult getting it out and somehow one of my fingers managed to touch the steel bit while it was still half plugged-in, the shock lasted for a good 4-5 seconds. I was really jittery (all over my body) for a few minutes, but other than the jittery feeling I felt absolutely fine. This has happened a few times over the years, but not in a long time. – jay_t55 Aug 18 '14 at 10:38
1  
As someone who has been through the same situation as Aeron (but shorter duration), I can confirm that, yes, it's unpleasant, and yes, it is frighteningly common, but no, it's not an instant fatality. Most likely, it didn't go deep enough to hit your heart, probably just the muscles of your arms. it's uncomfortable for a few minutes after it happens, but it doesn't kill if you're lucky. – Nate Kerkhofs Aug 18 '14 at 12:28

The paranoid way to use a non contact voltage tester is:

  • Test that outlet shows as live
  • Flip breaker
  • test that outlet shows as dead
  • Test a different outlet that should still be live

The last step is what would have saved you a shock here - its to check that your tester didn't die while you were flipping the breaker, and that you haven't done anything silly like forgetting to turn it on.

Though if it were a loose connection you still could be very unlucky and have it pass all those tests with the outlet still live.

share|improve this answer
1  
This is indeed the correct way of doing it. Verify the change, then verify the tool. – SQB Aug 17 '14 at 12:00

Step 1

1. Test.


Step 2

2. Confirm.


enter image description here

3. Do work.


Step 4

4. Check your work.


Always test the tester. (Preferably with a different tester.) NCV's should only be used to confirm an outlet should work, NOT that it is dead. They are also nice for locating CBs if you want to play the flip on/off game, though not to be used for confirmation of that either. Item 4, the outlet tester, would have alerted you to the live wire and it's incorrect wiring. It's a common curtsey in my crew to ask "Did you check it with a wiggy yet?" (item 2) for their own safety as they begin. We also never defer to each other, check it again yourself.

Once I have a box open I check all around with a NCV again. Most likely there are other wires from other circuits and depending on the situation those get shut-off too.


A note on NCVs:

They will sometimes pick up a strong enough induced current (from proximity to live wires) to give you a false positive. Again, non-contact voltage testers are best used to see if an outlet should be working, at a glance, NOT to confirm that it is dead.

More on Stack Exchange: Is a negative reading from a non-contact voltage detector sufficient?

share|improve this answer
1  
I agree with all of this but am wondering if they make a plug in tester for 240v outlet configurations used in the UK and do they have gfci protection for them? – user24125 Aug 17 '14 at 3:03
    
@user24125 I have no experience with UK power. A quick search found this: earthingoz.com.au/online-store/accessories/uk-outlet-tester I never had one so nifty so I assume the GFCI 'test' function on the one pictured just shorts the wires the same way the outlets button does, so you can redundantly test the outlet. Check your local giant hardware store. – Mazura Aug 17 '14 at 3:45
    
Thank you for the info. – user24125 Aug 17 '14 at 4:07
    
The GFCI test button shorts the live conductor to the ground conductor through a resistor. The point of the resistor is to provide just enough unbalanced current to trip the GFCI, but not enough to trip the breaker. Mine has a resistor that reads just under 18K ohms, which works out to be about 0.006 amps. – Brad Gilbert Aug 17 '14 at 15:37
1  
@user24125 I have a similar socket tester for UK sockets, a few quid from maplin years ago. It's handy for checking the polarity of sockets on campsite pitches - in France they're backwards at least 1/3 of the time, but if working in the power circuit I plug that in to the appropriate socket and can see what's going on as I walk up to it. I still check with another tool though (often a multimeter as soon as the wires are exposed). I'm lucky in that only the labelling is dodgy here, not the wiring. – Chris H Aug 18 '14 at 8:30

Unlucky to have come across a dodgy installation. What follows is a US experience, same voltage. We lived in a house dating from "Rural Electrification" so that might give you an idea of the age of the fuse panel. There was this coiled bit of Romex hanging off a nail in the eaves, bare clipped off ends, that was hot. After pulling all the fuses and the Range and Pump 220V fuse blocks, it still was hot. We had to call the power company to come pull the meter as it was wired for who knows what ungodly reason, into the input lugs to the fuse panel.

The experience shows why I prefer a standard contact voltmeter for verification, two different methods for cross-check. I love the non-contacts for ease of use.

share|improve this answer

Always verify the non-contact voltage tester is working properly, before trusting it (this is true for any tool, I guess). Aside from that, it just sounds like you were unlucky.

This is why it's important to know what you're doing, before attempting any DIY project. The person before you obviously did not, and the end result could have been your death (luckily it wasn't).

share|improve this answer
    
Agree completely - I like to think I'm more than comfortable with a variety of simple tasks, but would never proceed with something I wasn't confident with. – user24536 Aug 16 '14 at 13:03

I had an electric shock as a teenager - I grabbed the cable of a plug-in light, and the rubber insulation turned out to be broken exactly where my fingers were. My fingers bent involuntarily, making the grip stronger and I am still alive only because my mum managed to pull the plug out.

It is unforgettable experience, so I always shut off the entire property electrics before doing anything. I also make sure that nobody would turn it on by mistake while I am working - if there are old style breakers (the ones with a wire), I pull them out and keep them in my pocket. In my current house there are MCBs but there is also an isolation switch before the meter, so I turn it off and tie a piece of wire, which physically blocks it in the OFF position.

And to answer your question - sorry but I think it was not just a matter of bad luck (I am being polite here :) )

share|improve this answer

I use a multimeter and check all three pairs (live-neutral, live-ground, and neutral-ground) before doing anything. This lets me catch bad wiring, as well as things like a leak to ground that may not have a high enough voltage to trigger an NCV or other yes/no tester.

share|improve this answer

Your Answer

 
discard

By posting your answer, you agree to the privacy policy and terms of service.

Not the answer you're looking for? Browse other questions tagged or ask your own question.