I know a fire suppression systems is a good thing to have in one's home if you have anything that heats up, ie... a kiln.
Question is thus, what type of suppression system is best for each type of fire source. I know about water sprinklers and foam dispensers, but are there any others? And if so what are they used for. This is related to another previous question here
There are lots of different types of fire supression systems, some of which can be hazardous if people can't escape quickly (eg, inert gas systems which rely on forcing all of the oxygen out of the room), and thus aren't legal for residential applications, as if could kill you if you slept through it. – Joe Feb 9 '11 at 13:53
up vote 5 down vote accepted
I would say that your best bet is to go to a fire protection contractor and get their expertise, but I can give you a quick overview. Your system is comprised of a sensor, your pipes, and the type of sprinkler head you choose.
Sensor: at what stage of the fire do you want to douse it? In order from early to later detection: Incipient phase uses an ionizing detector. The smoldering phase, where smoke particles are visible, uses a photoelectric detector. The flame phase uses a UV or IR radiation detector. The heat phase uses a fusible sprinkler head that is set to activate the heads at a certain temperature above the ambient room temp. My house has a sprinkler system that uses fusible heads.
The pipes can either be a wet or a dry system. Basically, wet means you have water in the pipes, ready to go on signal. Good: quick when you need it. Bad, need a propylene glycol mix if you are in a zone that freezes (my garage, for instance). A dry system has empty pipes, which can either get filed by the fire department running water into the system or by a preaction system, where the water is stored in a tank, the detector sends a signal that the pipes should fill, then the individual sprinkler heads open up when needed in that section.
The sprinkler heads can be crafted to your situation. Like I mentioned before, you could have the fusible head run the show. You can also have a mist head, which will leave less water damage. A deluge system has open heads on dry pipes, which can flood the area if needed.
Now this all presupposes that water is what you want. I don't know what you are burning, but there are four classes of fires to fight: A is ordinary combustibles, B is flammable liquids and gasses, C is electrical and D is metals. For a burning liquid fire, for example, you certainly don't want water, you want those heads to release a foam to effectively smother the fire. CO2 would cool the flame, but that would cause problems if you were stuck in there, too.
Whatever has the potential to burn requires the triangle of oxygen, heat, and fuel. Remove one of those, and you have no more fire.
For your problem of the kiln, I guess I am having trouble picturing it. It seems like a lot of money and trouble to install a fire suppression system if it is a small pottery kiln. For a more industrial kiln, I don't know...Perhaps talk to the kiln's manufacturer and ask what their clients typically do for fire protection. I don't want to lead you on the path of something expensive and unnecessary. Good luck!
Great detailed answer. One customer of mine had a pottery shop in a rental space. The fire dept and code inspector had us install a simple thermo heads over the kiln.(personal protection type, not deluge type) We simply tapped the cold water feed from an adjacent bathroom, pex tubing to the heads in the kiln room. Cheap, easy and fast. But do check with local fire dept for advise. – shirlock homes Feb 9 '11 at 11:47
@shirlock - Pex for fire suppression? I thought those pipes had to be steel, or some type of metal with a higher melt point. – Tester101 Feb 9 '11 at 13:08
@shirlock -the kiln was an example not exactly what I have, but similar, small, really hot. – allindal Feb 9 '11 at 20:27
