I am in the middle of a deep energy retrofit of my house, and a quick-and-dirty online manual J calculation of the projected loads once my projects are completed shows an estimated heating and cooling load of only 13,000 BTUs, compared to the current baseline of 41,000 heating / 28,000 BTUs cooling.
Since this is such a small number, my existing 125,000 BTU furnace will become even more ludicrously oversized than it is now. So I'm considering replacing it with a single ductless mini-split heat pump.
Here's my quandry: the numbers alone say that a single-headed heat pump unit should easily be able to handle both the projected heating and cooling loads. But I'm worried about getting the conditioned air consistently into the three bedrooms, which in typical ranch house fashion, are on the other side of the house from the living area, accessed through a hallway. The living area will probably be fine, but I'm worried that the bedrooms might not get enough of the conditioned air, even with a sealed and well-insulated building envelope (R-26 walls, R-50 ceiling, R-20 footing insulation).
If a single unit will be enough, where should I put the unit? In the living area above the entrance to the hallway? If a single unit won't be enough, would a double-headed unit with a single outside compressor work? Where should I put the other unit?
Maybe. It depends on your climate, comfort range, and behavior.
You may be able to get away without supplemental heat sources if you can tolerate temperatures 10ºF or more above or below the setpoint and if you keep the bedroom doors open most of the time. Are you planning on installing an HRV or ERV? If so, that will help with mixing. Cooling can be more difficult to distribute because of solar gains. I'm writing mainly with heating in mind because that is my experience.
Note that even if your MSHP rated heating capacity is sufficient for your calculated heating load, you'll want to make sure it has enough capacity at the design temperature. Some units maintain capacity pretty well at cold temperatures (Mitsubishi FH series and Fujitsu RLS2-H series), but others do not.
Most people who attempt single-point-source heating with MSHPs install electric resistance heaters in other rooms and/or install a circulation fan to assist with mixing of air.
Supplement with electric resistance heaters
Common options here include electric baseboards, radiant cove heaters, and wall-mounted panel radiators (plug-in or hardwired). Occupant control here is key because you want to maximize usage of the MSHP and only use the resistance heaters when necessary.
For my 1000 sf ranch semi-deep energy retrofit with MSHP, I plan on installing radiant cove heaters in the bedrooms and bathroom. The bedroom heaters will be controlled by line voltage programmable thermostats (e.g. Honeywell P-8001) set lower than the MSHP, and only at night when bedroom doors will be closed. The bathroom heater will probably just get a cheap dial thermostat. Dana Dorsett on GBA talks about using occupancy sensors to control the radiant cove heaters.
Use a circulation fan to help mix air
Some people use low-wattage bath fans (e.g. Panasonic WhisperGreen) to pull air from the living space and supply it to the bedrooms. This still might not be enough to keep the bedrooms close to the heating setpoint because the supply air delta T is so small (only 5–10ºF). If you do room-by-room heat calcs (part of the official Manual J spreadsheet), you can compare the room design heat loads to the Q=1.08*CFM*DT for the circulation fan airflow, to help determine if this is sufficient or you need to supplement with electric resistance heaters.
Some people might not like having a bath fan grille in their living room, even if it is decorative. And running the ducts can be tricky, especially if your R-50 ceiling insulation is already installed. I'm thinking about installing a variable-speed in-line fan in my (unvented, conditioned) crawlspace to distribute air to the bedrooms from the living room. You can't beat the low-watt draw of the WhisperGreen bath fan though.
You probably would not want to use your existing furnace fan and ducts to help distribute the air because it is likely an inefficient motor and duct leakage would be bad if your ducts are in unconditioned space.
Location of single indoor head
In the main living area sounds like a good location. Here's what to think about:
  1. You want it to be able to "see" into as many rooms as possible.
  2. Length of the refrigerant lines running between the indoor and outdoor units is also a consideration. There's an efficiency penalty above 25 ft. The Mitsubishi comes pre-charged with refrigerant for up to 25 ft. Lines longer than that need more refrigerant to be added.
  3. Installation on exterior walls is much easier than interior walls.