I am running armored 12/2 bx to wire 4 high hats, the armored cable is grounded. There is a heating duct which I must go over, but the AC will come in contact with it... Is this ok or do I need to avoid having it make contact?

share|improve this question
add comment

4 Answers 4

Armored cable is meant to resist damage to the conductors from contact with other materials (like a duct). The armor itself is grounded when properly installed, and touching other metal should pose no risk (assuming the armor is not so bent or compressed as to expose the conductors).

share|improve this answer
add comment

There is no such thing as BX cable. Are you working with Type AC cable (armored cable), or Type MC cable (metal-clad cable)?

Metal-Clad Cable (Type MC)

Type MC cable has a grounding conductor, and the sheath cannot be used as a grounding conductor.

If you're working with MC cable, it's not likely any fault condition could lead to the ducting becoming energized.

Armored Cable (Type AC)

Type AC cable has an internal bonding strap, which is used as a grounding conductor.

If you're working with AC cable, there are indeed fault conditions where a duct in contact with the armor could become energized. I'd try to avoid contact between the sheath and metal objects. In either case, make sure the grounding strap is properly bonded.

NOTE: The fault conditions required to energize the ducting would be, improper bonding, and a ground fault (current flowing on the sheathing).

share|improve this answer
4  
"BX cable" is the product name of the original armoured cable, which has since been replaced by modern type AC. It's now used colloquially in the same way that "Romex®" (a brand name) is often used to refer to any Type NM cable.. in the same way people use "Kleenex®" to refer to any tissue paper. That said, when someone says "BX" it's not clear if it's AC or MC. In my region I typically only ever come across MC (I don't think the box stores even sell AC), and I used to always call that "BX" as everyone else I knew did. –  gregmac Apr 10 at 16:50
add comment

Apart from electrical considerations, one should avoid having dissimilar metals in long-term contact, especially in what could be damp or humid conditions. Electrolytic corrosion could compromise one or the other of the metals. That's why, for example, you need to use copper clamps and copper nails to fasten copper water pipe...

share|improve this answer
add comment

When properly installed the cladding of both AC and MC cables are always grounded (in most cases using identical connectors) and both cable types have always been installed in contact with most of the usual conductive building materials: steel studs, structural steel, ducts, plumbing and so on. And because Armored Cable has the bonding strip, its sheathing would have the lower resistance of the two cable types making it the safer one if its sheathing had to conduct a fault current.

Because many more people know exactly what you mean when you say Romex, I prefer the word. When it comes to the terms BX , AC or Armored Cable, it depends on who I'm talking to and it also depends on whether it's the old steel stuff or the contemporary aluminum. For the old stuff, because more people would know what I mean, I'd be more likely to say BX and reserve the terms AC or Armored Cable for only when referring to the newer stuff and talking to someone who knows what it is.

Why Armored Cable? Is this your home? Is it elsewhere wired in Romex? Why #12 awg? Is it a 20 amp circuit? What kind of Armored Cable do you have? Is the sheathing aluminum? Is there a full size bonding strip? Is there a green insulated copper ground conductor?

share|improve this answer