Main outdoor breaker is ONLY 100 AMP but total of Breakers AMP on internal panel is 165 AMPs. From what I have read so far this still ok. I could have Subpanels/Feeder Panels down stream from the main breaker requesting more output but if the Main is unable to handle it then it should "flip off" correct?

share|improve this question

marked as duplicate by Niall C. Feb 19 at 4:17

This question has been asked before and already has an answer. If those answers do not fully address your question, please ask a new question.

2  
See the section Summing Up Breaker Ratings Means Nothing in this answer to the question, Do the breaker amp readings sum up to dictate my current panels total / possible amperage? –  Tester101 Feb 18 at 11:59

1 Answer 1

Synopsis: The sum of all the branch circuit breakers is a meaningless number.

The main breaker will "trip", or "flip off" as you say, when the current (amperage) load well exceeds it's rating for a predetermined amount of time. Meaning a breaker does not trip when the load is 1 or 2 more than the rating. The "continuous load" on the panel should not exceed 80%. In a residential application this is a hard number to pin down though.

As to your sub-panel question, a load calculation is the only accurate way to tell if your service is adequate to support any new loads on the service.