I'm running 2" PVC from my house to a detached garage to run a 60 amp feeder. Looking at the NEC, it looks like I need to put it in SCH 40 below-ground. However, it looks like I have to use SCH 80 anywhere the PVC will be above the ground. Is that correct, or can I get away with using SCH 40 for the whole run?

share|improve this question
    
When I ran power to my shed about 10 years ago I used EMT. It was about as cheap as PVC and I don't have to worry about anyone accidentally digging and hitting a live wire. I put it down about 2 feet. No problem to date. –  getterdun Feb 12 at 4:56

2 Answers 2

National Electrical Code 2014

Article 352 - Rigid Polyvinyl Chloride Conduit: Type PVC

II. Installation

352.10 Uses Permitted. The use of PVC conduit shall be permitted in accordance with 352.10(A) through (H).

(F) Exposed. PVC conduit shall be permitted for exposed work. PVC conduit used exposed in areas of physical damage shall be identified for the use.

(G) Underground Installations. For underground installations, homogenous and nonhomogenous PVC shall be permitted for direct burial and underground encased in concrete. See 300.5 and 300.50.

Article 300 - Wiring Methods

I. General Requirements

300.5 Underground Installations.

(D) Protection from Damage. Direct-buried conductors and cables shall be protected from damage in accordance with 300.5(D)(1) through (D)(4).

(4) Enclosure or Raceway Damage. Where the enclosure or raceway is subject to physical damage, the conductors shall be installed in rigid metal conduit, intermediate metal conduit, Schedule 80 PVC conduit, or equivalent.

352.10(F) says that the PVC conduit "used exposed in areas of physical damage shall be identified for the use". I know schedule 80 is suitable for protection from physical damage, however, the Authority having jurisdiction in your area may allow schedule 40 as well. You'll want to check with your local inspector to be sure, or use schedule 80 for the exposed section.

300.5(D)(4) says that even though the conduit is buried, if it's subject to physical damage (not deep enough, under a garden, etc.) it still has to be schedule 80.

UL 651

Schedule 40, 80, Type EB and A Rigid PVC Conduit and Fittings

1.2 Schedule 40 and 80 conduit and fittings

1.2.1 Schedule 40 rigid PVC conduit and fittings are for aboveground use indoors or outdoors exposed to sunlight and weather, and for underground use by direct burial or encasement in concrete. Schedule 40 rigid PVC conduit, elbows, that are specifically marked for underground use are suitable for use underground only by direct burial or encasement in concrete.

The UL listing says both 80 and 40 can be used in both above and underground installations.

Guide Information for Electrical Equipment The White Book 2013

Rigid Nonmetallic PVC Conduit (DZYR)

Use and Installation

Schedule 40 conduit is suitable for underground use by direct burial or encasement in concrete. Schedule 40 conduit marked "Directional Boring""(or "Dir. Boring") is suitable for underground directional boring applications. Schedule 40 conduit is also suitable for aboveground use indoors or outdoors exposed to sunlight and weather where not subject to physical damage. Schedule 40 conduit marked "Underground Use Only" is only suitable for underground applications.

Schedule 80 conduit has a reduced cross-sectional area available for wiring space and is suitable for use wherever Schedule 40 conduit may be used. The marking "Schedule 80 PVC" identifies conduit suitable for use where exposed to physical damage and for installation on poles in accordance with the NEC.

The White Book clearly states that only schedule 80 is suitable for use where exposed to physical damage, though again, says schedule 40 is suitable for aboveground use (unless labeled otherwise). So while you may be able to use schedule 40 for the entire run, you'll have to use schedule 80 through any areas where the AHJ deems the conduit is exposed to physical damage.

share|improve this answer
up vote 0 down vote accepted

I asked the local inspector, and he said SCH 40 is fine for both above and below ground. I ended up using 2-2-2-4 Aluminum (marketed as mobile home feeder) to support the 60 amp service.