I purchased 2 hanging lights from Ikea and they are wired with plugs. I was wondering if I could run the cords with the plugs through the attic and down the wall to the plug. Will the wire get to hot in the summer and cause a fire?

share|improve this question
    
Do you have electrical boxes in your ceiling? If you do, you can just snip off the plug and wire it directly. –  Steven Jan 27 at 17:46
3  
@Steven Or you could mount an outlet in the ceiling box and plug it in. Solves the problem of devising a safe box cover. –  bib Jan 27 at 18:00
1  
You absolutely can not do it the way you're describing. NEC 400.8 Uses Not Permitted (ref. Extension Cord) Flexible cords and cables shall not be used for the following: (1) As a substitute for the fixed wiring of a structure (2) Where run through holes in walls, structural ceilings, suspended ceilings, dropped ceilings, or floors (5) Where concealed by walls, floors, or ceilings or located above suspended or dropped ceilings –  gregmac Jan 27 at 18:46
    
@gregmac Notice 400.8 Uses Not Permitted. Unless specifically permitted in 400.7, flexible cords and cables shall not be used for the following.... 400.7 allows for (2) Wiring of luminaires (fixtures). Would this not qualify as a luminaire? –  crush Jan 27 at 20:49
2  
@crush Sometimes the language is not very explicit, so you have to understand the intentions and reasoning of the authors. Maybe it's just me, but lamp cord in the walls doesn't sound good. –  Tester101 Jan 28 at 13:59

1 Answer 1

Short answer: No, you can't run flexible cord through the ceiling/walls.

There are many problems with this, the main being that it's against code, relevant section:

NEC 400.8 Uses Not Permitted

(ref. Extension Cord) Flexible cords and cables shall not be used for the following:

  1. As a substitute for the fixed wiring of a structure
  2. Where run through holes in walls, structural ceilings, suspended ceilings, dropped ceilings, or floors
  3. Where concealed by walls, floors, or ceilings or located above suspended or dropped ceilings

Essentially, you can use flexible cord from the junction box to the light itself (NEC 400.7, ref Pendants), but not past that point where it becomes part of the "fixed wiring of a structure". The main reason (as I understand) for this is that flexible cord is more subject to physical damage (which can then lead to overheating).


You have a few options.

Suspend the lights

You can suspend the lamp from the ceiling using hooks or some other physical means, so long as the flexible cord is exposed (eg: no holes through drywall).

enter image description here

Use surface-mount conduit

There are various surface-mount conduits (or raceways) products that will allow you to partially conceal the wires. Some products can be painted.

enter image description here

Add a junction box

Bottom line, if you want the wire totally concealed, you need a junction box. This is a non-trivial task, and almost certainly involves punching holes in the drywall (which you'll have to patch afterwards) to be able to fish wires. You'd use solid-core wire to comply with code to run to the junction box (typically 14/2 romex).

How to actually do this warrants an entirely new question.

Anyway, once you have a junction box in the ceiling, the best thing is to get a type of lamp designed to be hard-wired.

enter image description here enter image description here

I looked around for a retrofit box cover to use the existing lights as hardwired, but can't find one. I'm not sure such a thing exists, but if it does, you could use that to use the existing lights as hardwired lights. Even in this case, the wire to the junction box has to meet code (eg, you can't use flexible cord), although it would be fine, as per NEC 400.7(1) to use flexible cord from the junction to the light fixture itself.

share|improve this answer
1  
Just a small annotation to this answer, if you go the junction box route (I always go this route), make sure that you get a junction box that comes with a brace which can support the weight of your fixture. Most kits will say on their packaging how much weight they are rated to support. Also, make sure you run the appropriate cable to the junction box. You can't, for example, run your lamp cable through the junction box simply because you now have a junction box. You'll want to tie Romex cable back to the switch. Use the same gauge as is running to the switch. –  crush Jan 29 at 17:41
    
Junction box might seem like overkill for your Ikea lamp, but what happens when you decide to upgrade to something nicer in the future that is of a little heavier construction? Something to consider. –  crush Jan 29 at 17:44