I have rewired the first 2 outlet in a circuit with 14-2 wire. However, I do NOT want to rewire the rest of the circuit because it is inside non-accessible walls. The rest of the circuit is a front door light with switch and an upstairs outlet. Is it okay to re-connect the new 14-2 with to old non-grounded, cloth-covered with 2 wires?

share|improve this question

1 Answer 1

If the 2 prong receptacles are existing receptacles, there shouldn't be a problem. As long as you realize the 2 prong receptacles will not have a ground, and you don't replace the 2 prong receptacles with 3 prong receptacles.