If I'm adding some new receptacles to a garage, and the wiring will be run surface-mounted to walls and ceilings, I think protecting the wiring with EMT conduit is probably a wise way to go.

I'm seeing some conflicting information as to whether it's OK to run NM-B (e.g. romex) inside EMT tubing. The more typical application is individual THHN conductors inside EMT. Rather than having to buy two types of wiring, is it OK to run the NM-B inside the EMT? Are there any special considerations?

share|improve this question

marked as duplicate by Tester101 Dec 21 '13 at 13:16

This question has been asked before and already has an answer. If those answers do not fully address your question, please ask a new question.

    
Possible. I answered it as I had some additional info specific to his garage installation. –  Edwin Dec 20 '13 at 23:35

1 Answer 1

In full EMT installations, it would be very hard to pull romex through EMT. Also, if you need to rewire or add additional wires, it would be near impossible to do without taking everything apart. It's definitely okay to do, in fact it's required to protect cable from damage.

2008 NEC - 334.15 Exposed Work says, "Cable shall be protected from physical damage where necessary by rigid metal conduit, intermediate metal conduit, electrical metallic tubing. . . ." See also Can Romex (NM-B) be run through conduit?

An option, which may be appropriate for you, is you can run regular NM-B along the wall close to the ceiling, and come down to your box with EMT. This way your cable is protected from physical damage where it's needed, but you don't need a full EMT installation. They make clamps which secure NM cable to EMT ends. You don't want to overfill your conduit, as heat build might be an issue.

enter image description here

In my experience wiring my house, in the end I found it was best to do a full EMT installation and run THHN though it. It is frustrating that 500 feet of White/Black/Green 12 gauge THHN is not cheaper than 500 feet of 12/2 Romex.

share|improve this answer