The instructions for the humidifier I'm installing says to connect the humidistat wiring to the two terminals "marked 24 VAC IN". My furnace doesn't have terminals marked that.

I have R,C,W,Y.G. Am I out of luck or is this just different terminology for the terminals I already have?

share|improve this question
    
Please include the make and model of the furnace. –  Tester101 Nov 18 '13 at 13:45
add comment

3 Answers 3

up vote 1 down vote accepted

Your furnaces controller is typically powered from a 24VAC transformer. Trace the incoming line-voltage power source - it should connect to a transformer. You can verify the output voltage is 24VAC with a multi-meter. Even if there is not a dedicated terminal, you can connect to the transformer output in parallel in order to power your humidifier. Often there will be a wirenut already present, but if not you can cut the transformer output leads, strip both ends and as well your output to your humidifier and connect all the stripped ends with a wirenut or other sutiable connector.

Alternatively you can power it with a dedicated 24VAC transformer.

share|improve this answer
1  
Wiring the humidistat directly to the 24V transformer, will cause the humidifier to become active whenever the humidistat says. This is not ideal, since the humidifier needs airflow to work. The humidifier should only be active when humidity is low and the blower is on. –  Tester101 Nov 19 '13 at 12:30
add comment

This is going to completely depend on the make and model furnace you have. If you simply wire the humidistat to the 24V transformer, the humidifier will be active only based on the humidistat. This is not ideal, since the furnace has to be moving air for the humidifier to function properly. You want the humidifier to be active when the humidistat is closed (calling for humidity), and the furnace is on.

Locate the control terminals

If you check the schematic on the furnace (often found on the inside of the access panel cover), you may find there are separate terminals on the control board for a humidifier. In some models these are 24V terminals, in others they're line voltage.

24 volt terminals

If they're 24V terminals, you're in luck. All you have to do is connect the humidistat wiring to these terminals, and you're done.

Line voltage terminals

If they're line voltage terminals, you're going to need a second step down transformer. You'll connect the primary side of the transformer to the terminals on the control board, then connect the humidistat to the secondary side of the transformer.

No humidifier control terminals

If there are no humidifier control terminals present, you'll have to get creative. Check the furnaces user manual, as it may have instructions on how to connect a humidifier. Though a common solution to this problem, is to connect one wire to the C terminal, and the other to the W terminal. This causes the humidifier to be active only when the furnace is calling for heat.

NOTES:
- Always follow all manufacturer installation instructions.
- Do not forget to turn off the power to the furnace while working.

share|improve this answer
    
This is promising. I've got no humidifier controls. So from your answer, connect C,W. I know W is the relay for the heat. What's C? –  kareem Nov 18 '13 at 3:36
    
Ah. Common/Ground. Got it. So now it can turn on when the heat is on. Does that mean it can't be used in the summer when the A/C is used? –  kareem Nov 18 '13 at 3:51
    
@kareem If you want it to also be active when the A/C is on, you'll have to find a way to switch between the W and Y terminals. So you'll use W in the winter, an Y in the summer. However, humidifiers aren't typically used with air conditioning. –  Tester101 Nov 18 '13 at 12:21
add comment

R + C = constant 24x7 24vac

Use these lines only if your humidifier has an electronics board that needs a constant supply of power separate from call for humidity.

In addition to constant power you will need some way to switch it on and off so that humidifier is humidifying only when humidity is called for. I recommend investing in a thermostat with humidifier control built in and let it and or your programming of it figure out when to turn on and off rather than sensing W/Y/G especially if you have a need for humidity + AC during summer Honeywell and others have intelligence to safely support this without rusting out your duct work.

share|improve this answer