The following picture shows a Honeywell T6360 Room Thermostat wiring connections. You will note they are numbered in the order 2 3 4 1 5 6. enter image description here
The Installation Instructions that accompany this unit, contains the wiring diagram below. In this diagram, the connections are numbered in the order 1 2 3 4. This is very confusing and I'm not sure if I should copy the positioning from the installation guide or connect to the marked numbers (even though they are out of position).
What is the correct way to proceed?
Click for full size image
up vote 5 down vote accepted
Use the numbers.
The position of the terminals in the wiring diagram is likely just for ease of drawing, and may not exactly model the actual device.
Wired and working thanks. Additional tip. There was a more accurate wiring diagram (positionally correct) on a sticker stuck on the back of the stat faceplate. – bentayloruk Nov 16 '13 at 12:14
  1. connect the heater cables at terminals 3 and 2.
  2. then check the power from socket with tester and connect that one with terminal 1.
  3. the other one is neutral and should be connected at terminal 2.