I'm re-wiring parts of my house and have pulled some 12/2 out. Is it against NEC code to re-use that cable?

I didn't have to pull that hard to get the cable out and there doesn't appear to be any surface damage or major bends. The cable is twelve years old from the time the house was built.

share|improve this question
2  
I don't believe there is anything in the NEC that says the cable has to be new. –  Tester101 Oct 13 '13 at 12:43
1  
But after looking at the search 'NEC code wire reuse', I think the NEC code might require that the wire is up to code for use that you are installing it for. Same type of requirements as if the cable was new. I think that you might have some issue with that being a 12/2 cable with regard to grounding, unless that cable is going to be installed in conduit that will be used as the grounding conductor which it might have been installed in before it was removed. –  Dan D. Oct 14 '13 at 4:33
    
Ah... Dan D. has a good point. If it's 12/2 cable without a grounding conductor, you'll not be able to reuse it since you'll need a grounding conductor to meet code. –  Tester101 Oct 14 '13 at 10:15

2 Answers 2

No, nothing is wrong with re-using cable and cable assemblies that are listed and approved provided that they are in working order and still permissible for new construction in the location that you intend to use them. Don't use a cable that doesn't have a grounding conductor would be the main rule for re-using what you'd find in a residential setting.

Re-use becomes more of an issue when you get into classified locations, such as medical facilities and other commercial areas. You wouldn't be able to re-use a bunch of MC (metal clad) cable where HCFC (hospital care facility cable) is now required - but you're not likely to run into those situations in a residential setting.

If it's the right type of cable, just test it:

  • Are the conductors stiff and brittle?
  • Is any bonding that used to be in the assembly still there, and in good shape?
  • Is the exterior obviously stressed, or showing signs of damage from smoke or water?

... don't use it :) Otherwise, you should be fine.

Still, even if it looks / tests fine - consider replacing it if it's over 15 years old. You need not waste it, Romex has oodles of uses out of the wall (it's great for tying up/down all kinds of stuff, for instance).

share|improve this answer

I went ahead and re-used the cable. There have been no issues so far but I may pull it back out and just go ahead and use new cable. Once I started installing the outlet I noticed that the plastic surrounding the solid wires was drying out and becoming brittle. The coating could easily crack when you bent the wires back into the box. Not sure if this is an issue all cable shows after 10+ years or if this is particularly low quality romex..

share|improve this answer

Your Answer

 
discard

By posting your answer, you agree to the privacy policy and terms of service.

Not the answer you're looking for? Browse other questions tagged or ask your own question.