I need to run a 50 amp circuit (120/240V) from a shed to a travel trailer that is permanently in place.

The previous trailer had 30 amp 120V service running underground to a mounted/covered outlet under the trailer and then the standard trailer cable/plug into that.

The run is ~50 ft. Running the 30 amp 120V service was fairly straightforward (big box hardware stores have the right wired for burying). But when I start looking at 50 amp things get less straightforward (to me).

I'm assuming from a brief googling of big box stores have not resulted in any results for #6 non-conduit buriable wire. So this leads me to believe that I need to run it in conduit, but then I get concerned about heat (this may be an incorrect understanding).

We only occupy the travel trailer 2 - 3 days a week for May/Jun/Jul/Aug/Sept. Most of the days are spent outside and the AC & oven will rarely be used. (I understand that you should plan for the largest load not smallest).

Can I run 50 amp (120/240V) underground? Do I need to ground the chassis of the trailer to a 8ft grounding rod? Should I use #4 instead of #6 to reduce the heat concern?

share|improve this question
2  
Both Lowes, and Home Depot advertise 6/3 UF cable, though Lowes seems to only sell it by the foot. Are you asking how to run the cable, or where you can buy it? –  Tester101 Oct 1 '13 at 14:31
    
At $4 per foot, you won't want to buy a lot of extra "just in case". Measure carefully at least three times. –  wallyk Oct 1 '13 at 16:05
    
Thank you all. It is so obvious on their pages now. Not sure how I missed it. $4/foot is crazy, but I understand why. Thanks much. –  Wayne Arthurton Oct 1 '13 at 16:10
    
Aluminum is usually far cheaper than copper. –  Jay Bazuzi Oct 2 '13 at 20:45
1  
If you go through the trouble of digging a trench for this new wire, bury several conduits instead of burying wire directly. You can then use them for a fresh water line, a sewer line out of a macerator, an additional circuit, telephone, ethernet, compressed air, etc. –  Jay Bazuzi Oct 2 '13 at 20:47
show 3 more comments

1 Answer 1

up vote 10 down vote accepted

Cable

The cable you're looking for is Type UF, or Underground Feeder cable.

enter image description here

It can be purchased at big orange, and big blue, by the foot. It's available in 6/2, 6/2 with ground, 6/3, and 6/3 with ground, and is rated for direct burial.

Attachment to Service

There is one temporary, and two permanent ways to supply power to a park trailer.

Temporary

Power-Supply Cord

You'll want to use a NEMA 14-50 receptacle, and 4 wire cord with NEMA 14-50 plug to connect the trailer to the service. The trailer's electrical grounding will be through the service plug, so only the distribution panel will have to be grounded.

enter image description here

Permanent

Mast Weatherhead

You can use four continuously insulated, color-coded feeder conductors strung from a mast to a weatherhead as a permanent feeder.

enter image description here

Raceway

A metal raceway, rigid nonmetallic conduit, or liquidtight flexible nonmetallic conduit, from the disconnecting means to a junction box on the underside of the trailer can serve as a pathway to run permanently attached feeders.

enter image description here

NEC

For reference, park trailers are covered in article 552 of the National Electrical Code.

share|improve this answer
    
Thank you. It is so obvious on their pages now. Not sure how I missed it. $4/foot is crazy, but I understand why. Thanks much. –  Wayne Arthurton Oct 1 '13 at 16:10
    
If the cable is buried does it need to also be in conduit? –  The Evil Greebo Oct 1 '13 at 16:21
    
@TheEvilGreebo No. –  Tester101 Oct 1 '13 at 16:23
3  
@TheEvilGreebo If you need more questions answered, please deposit another $0.25. –  Tester101 Oct 1 '13 at 16:25
1  
When you run it underground, it's a good idea to also bury a marker several inches above it (often a red poly tape that says something like "CAUTION: Buried electric line below"). This helps prevent anyone who is digging from hitting it. You also need to use conduit above the minimum burial depth including when it's above ground. –  gregmac Oct 1 '13 at 21:22