I removed a ceiling fan and capped off both wires but my circuit breaker trips. Is it possible that the fan was in a pathway with some thing else? If so, do I just connect those wires together? There are two white wires and one black wire.

share|improve this question
4  
Did you cap them together? –  The Evil Greebo Sep 19 '13 at 16:31

1 Answer 1

It sounds like you capped 2 whites together, which would be logical.

However, you've probably discovered a situation where one of the whites is a switched hot, improperly labeled (i.e. not labeled).

Try putting a cap on each wire by itself.

It's unlikely that putting a break in a circuit would cause a trip. It's the opposite problem, a short that causes a trip.

share|improve this answer