What ampacity circuit breaker would I need for an 18 amp electric heater?
Here's a link to the model (IEP-4024), it's North American, 240 volts, 4000 watts, installing it outdoor.
The rule of thumb is to multiply the listed amps by 1.25, thus ensuring that the load is 80% of the rated capacity. Although, the installation instructions clearly state: "Electrical connection must be per formed by a qualified elec trical tradesperson. Installation must conform with the latest editi on Electrical Code ANSI/NFPA N0 70 in the U.S.A. and PART 1 CSA C22.1 in Canada. " – Chris Cudmore Sep 18 '13 at 14:48
RTFM
After reading the user manual for this heater, as per National Electrical Code.
National Electrical Code 2011
ARTICLE 110 Requirements for Electrical Installations
I. General
110.3 Examination, Identification, Installation, and Use of Equipment.
(B) Installation and Use. Listed or labeled equipment shall be installed and used in accordance with any instructions included in the listing or labeling.
It appears that it has subdivided heating elements, which requires 2 separate 240 volt 9 ampere branch circuits. It also states that "the electrical connection must be performed by a qualified tradesperson.".
Connect each lamp circuit to a 230 - 240 Vac, 60Hz, 9 Amp copper wire circuit that is properly grounded. Electrical connection must be performed by a qualified electrical tradesperson.
Installation must conform with the latest edition Electrical Code ANSI/NFPA N0 70 in the U.S.A. and PART 1 CSA C22.1 in Canada.
Wiring Diagram from User Manual
Select the Conductors
Since you're dealing with space heating equipment, you'll want to check article 424 of the NEC. In article 424, you'll find that the conductors have to be sized to 125% of the load served.
ARTICLE 424 Fixed Electric Space-Heating Equipment
III. Control and Protection of Fixed Electric Space-Heating Equipment
424.22 Overcurrent Protection.
(E) Conductors for Subdivided Loads. Field-wired conductors between the heater and the supplementary overcurrent protective devices shall be sized at not less than 125 percent of the load served. The supplementary overcurrent protective devices specified in 424.22(C) shall protect these conductors in accordance with 240.4.
So you'll have to do a bit of math to figure out the minimum ampacity of the conductors.
9 amperes * 125% = 11.25 amperes
Now that you know the minimum ampacity required, you'll want to check article 310.15 to figure out what size wire you need. A quick look at table 310.15(B)(16), shows that 14 AWG wire is good for 15 amperes at 60°C.
Select the Overcurrent Protection Device
Now that you've selected the wire size, you can choose your overcurrent protection device. In this case, you'll want 2 15 ampere dual pole circuit breakers.
Wiring the Circuits
When it comes to wiring the circuit, you have a couple choices. You can pull two 14/2 with ground cables from the panel to the outlet, or you can pull a single 14/2/2 with ground cable.
14/2 NM-B cable14/2/2 NM-B cable
Two 14/2 with Ground
Pull two 14/2 with ground cables from the panel to the outlet, and connect the heater as follows:
14/2 wiring
Don't forget to reidentify the white conductors, by marking them in an approved manner.
One 14/2/2 with Ground
A 14/2/2 with ground cable consists of a black, red, white, white with red stripe, and a bare conductor. The only drawback here, would be that since there are more than 3 current carrying conductors, the conductors have to be derated by 80%. Even with the derating, the conductors are still rated for 12 amperes at 60°C. Which is still above the 11.25 amperes required by the circuit, so there should be no problem using this cable (as long as the run is not overly long).
14/2/2 wiring
Again, don't forget to reidentify the white conductors.
You're asking the wrong question.
The circuit breaker size is based on the wiring size, not on the application size. The purpose of the circuit breaker is to protect the wiring from fire.
A better question would be "what size wiring do I need for an 18 amp load?" Then you can work out the circuit breaker, receptacle, etc. afterward, based on @HerrBag's comment.
If you just swap out an existing 15 amp breaker for a 20 amp one because your electric heater keeps tripping it, it's likely that your wire will be undersized for the application and you've created a very serious fire risk.
Simply put, What size circuit do I need for an 18 amp device? The breaker and wire size follow. – bib Sep 18 '13 at 0:04
While this does make a valid point, it does not answer the question. – Tester101 Sep 18 '13 at 9:58
You can't just swap a 15 amp breaker with a 20 amp breaker, unless the wire is 12 gauge or bigger (smaller gauge number) – Brad Gilbert Sep 19 '13 at 2:16
In America the NEC requires 125% protection of circuit so if you have an 18 amp heater then you would need to account for 23.4 amp. Meaning you would need a 30 amp circuit breaker and 10 gauge wiring.
Can you cite the code section? – Tester101 Sep 18 '13 at 9:54
@Tester101 - 215.2(A)(1) - for continuous loads - which a heater would fall into that category. – DMoore Sep 18 '13 at 15:58