This seems like a simple question, but I cannot seem to find the answer in the 2008 NEC.
There are references to "maintaining spacing" in many sections of the code such as the following:
310.15.B.3.a
(a) More Than Three Current-Carrying Conductors in a Raceway or Cable. Where the number of current-carrying conductors in a raceway or cable exceeds three, or where single conductors or multiconductor cables are installed without maintaining spacing for a continuous length longer than 600 mm (24 in.) and are not installed in raceways, the allowable ampacity of each conductor shall be reduced as shown in Table 310.15(B)(3)(a). Each current-carrying conductor of a paralleled set of conductors shall be counted as a current-carrying conductor.
For the life of me, I cannot find what "proper spacing" is for two wires run in parallel in free air. At the moment, I am most interested in the answer for NM-type wiring, but it would be good to have a reference for all types of wiring if possible.
Here is an example from the NEC for multiconductors in cable trays where I am hoping someone knows of an equivalent section that defines proper maintained spacing for free-air:
392.80.A.1.c
(c) Where multiconductor cables are installed in a single layer in uncovered trays, with a maintained spacing of not less than one cable diameter between cables, the ampacity shall not exceed the allowable ambient temperature-corrected ampacities of multiconductor cables, with not more than three insulated conductors rated 0 through 2000 volts in free air, in accordance with 310.15(C).
This is a "mike holt forum" depth of question. – Bryce Aug 12 '13 at 18:44
From Mike Holt Forum. "That is the million dollar question. I just keep them from touching. Keep in mind that you can have 4- 2 wire nm cables stacked without being hurt by the derating that is necessary." – Tester101 Aug 12 '13 at 19:11
@Tester101 Thank you for the leg work on that. If you want to put your comment into an answer and explicitly indicate that it is not currently defined, I will accept your answer. – user14416 Aug 12 '13 at 19:18
I would interpret that as referring to cables are run in such a way that nothing would prevent them from sitting against each other. – supercat Jan 20 '15 at 22:08
up vote 1 down vote accepted
The National Electrical Code (NEC) does not define the proper spacing that should be maintained.
A similar question was asked, and answered on the Mike Holt Forum.
Spacing for single insulated conductors in cable trays, is in art.392.80(A)(2)(c) and (d).
-1 This may not answer the question. At a minimum, the referenced code should be quoted here. – BMitch Aug 15 '15 at 19:11