Can 2 romex cables be stripped before entering an EMT to allow more conductors in a 1/2" EMT? How would you transition from Romex to individual conductors going in or out of the EMT? Or is that allowed?
The wires inside Romex are THHN type, which is okay for EMT, but you cannot use a bare copper wire inside EMT. I would transition from Romex cable to EMT with a metal box. Bond the bare copper wires to the box with a grounding pigtail, and add a insulated green THHN wire to continue the ground through the EMT.
I don't believe you can -- my understanding was that the wires have to be individually labeled and I didn't think the wires inside Romex were individually labeled? I could be wrong though. There are also limitations to the number of wires you can have inside a 1/2" EMT as well. – Jacob S Jul 18 '13 at 17:44
Apparently the size of a romex when in an EMT is calculated rather strangely. The width of the flat Romex represents the diameter and the volume is calculated as if it is a complete circle which dramatically reduces the amount of Romex permitted in the EMT. Far more THHN would be permitted. At least that's the info I've found. @Edwin Thanks, very helpful. Jacob S I appreciate the info. Thanks – BobJax Jul 18 '13 at 18:05