I am trying to create a computer charging station. I have many laptops and Android Tablets that I would like to charge at once. Assuming I wire it correctly, how many adapters can I put on 1 plug?
Laptops are 40W charger cords.
Tablets are 10W charging blocks.
The figures you quote are for the "output" of the chargers. What are the specs for their inputs? They'll likely be listed as some amount of current at some particular voltage. Do you how much current your circuit can deliver? In the USA, it would be either 15 or 20 A. – Pigrew Aug 22 '13 at 4:29
36 laptops,
or
144 tablets,
or
18 laptops and 72 tablets,
or
Any combination of laptop and tablet that is less than or equal to 1440 watts.
Since a 15 ampere 120 volt circuit can supply a maximum of 1800 watts, but a circuit should only be loaded at 80%.
15 amperes * 120 volts = 1800 watts
1800 watts * 0.80 = 1440 watts
This example assumes that this is a dedicated circuit, with no other loads on the circuit.
Dedicated 20A circuit - 1920 watts – Fiasco Labs Jul 13 '13 at 14:50
+1 But that assumes that nothing else is on the circuit (and remember that, in almost all cases, not just one outlet is on the circuit). If other things share the line, adjust accordingly. – bib Jul 13 '13 at 17:18
You really shouldn't assume a country when answering questions like this. – user13406 Jul 13 '13 at 18:28
@bib Please see the small print at the bottom of the post. – Tester101 Jul 14 '13 at 0:18
@Lee I show the maths, so it can easily be applied to any country as long as you know the voltage and amperage. – Tester101 Jul 14 '13 at 0:20
It depends on which country you're in, and its electrical circuits. Basically, a certain number of sockets will be connected to one circuit in your electricity box (the fuse and switch box, where the mains comes into your house and is connected up to the different sockets / lights / cookers etc. through fuses).
Some people above have given you the ratings for 120V US sockets. In the UK, it's 240V and up to about 3KW, so you can roughly scale these accordingly. BUT, bear in mind that the voltages are different and need conversion (see Ohms Law) and, don't forget to count anything on the same circuit that's already using power. For example, if you hook all this up and it runs at the maximum load, but then your tumble dryer switches on, on the same circuit, you'll be in trouble.
If there are no other loads on the circuit, you can pull 15 amps @ 120VAC = 1800 watts per circuit. Let's say 1500 watts to have some headroom.
You can easily figure out how many laptops or tablets you could charge at once.
Circuits should only be loaded to 80%, which would be 1440 watts on a 15 ampere circuit. – Tester101 Jul 13 '13 at 14:08
It does not depend up on your load, it depends on your installation computer charging station wire size. 0.5, 1.0, 1.5, 2.5 core wire. If you want a 6 amp load connect supply then you use 0.5 core wire. 1 core is used for 8-10 amp current.