I am trying to replace my existing thermostat.
My old thermostat has:
Rh, W (coming from the heating unit).
Rc, Y, G (coming from the AC unit).
On the Venstar T5800, I can map as follows:
Rh+Rc -> R
W -> W
Y -> Y
G -> G
Now I need to add a common wire. HVAC tech tried to put a jumper between R and C. Venstar started up, the screen went on, but then the moment the AC turned on,the unit shut itself off. Is this a problem with the thermostat or with the way the HVAC guy set it up?
I bought an ELK 24V AC dedicated supply/transformer. Now I have two wires coming off it. It is running to my thermostat. How do I connect them? Does one wire from the supply/transformer go in to C and the other in to R, in addition to the Rc and Rh wires already in the R?
i.e. the following:
ACSupply1 -> C
Rh+Rc+ACSupply2 -> R
W -> W
Y -> Y
G -> G
Or would this not be recommended?
Any help with this would be very much appreciated. As you can see, I definitely need it.
the answer on this question might help. – Tester101 Jul 5 '13 at 16:51
The power supply trick is a hack, not a proper wiring technique. – Tester101 Jul 5 '13 at 16:54
The picture below you would pull the green wire off of Green at both the stat and furnace and move it to C/Common, then you jumper Yellow to Green at the furnace.