I have two bathroom exhaust fans that need to be vented out of the house, but I'd like to do it using a single wall penetration. Is there a code compliant, safe way to do this?

  • Both bathrooms are on the same level of the house.
  • There is no guarantee that both fans will be the same type, size, power, etc.
  • Each fan runs independently of the other.
  • Pipe runs will be different lengths from fan to exit point.
  • Fans are on separate electrical circuits.
share|improve this question
    
Nothing in the IRC actually touches on this. I have though had inspectors tell me they wouldn't pass if I did it and I have seen exhausts vent to the soffit vents pass... I did have a friend who did this and he said that every once in a while you would get a whiff of a dump from the other bathroom. Personally I would rather vent one to the attic then tie them together. –  DMoore May 17 '13 at 21:39
    
Anything is possible for a Possible –  Jason May 18 '13 at 16:33
1  
@Tester101 "Shop for me" type questions are not on topic here, douche! –  Tester101 May 20 '13 at 15:34
    
This isn't really a SFM question. It's How the heck do I do this? –  Chris Cudmore May 21 '13 at 20:17
    
If we figure out the answer to this - I would like to have three going to one! –  DMoore May 22 '13 at 20:57
add comment

2 Answers 2

I don't know about code compliance. But, this might work for you:

1 Y-Connector at the outside vent.

enter image description here

2 Backdraft Dampers (one on each leg) at the Y to stop the backflow of noxious gases from one fan(on) to the other (off).

enter image description here

Note that the backdraft dampers will add to the resistance of the duct work. You may wish to move up to the next size of duct.

share|improve this answer
    
What if both fans are on at the same time, do I have to double the size of the outlet on the wye to compensate? –  Tester101 May 17 '13 at 14:34
    
I don't think so. Pressure and velocity should increase to compensate somewhat. 5" duct is 1.5 times bigger than a 4" (and a 6" is 1.5 times bigger than a 5") so that would probably mitigate. But we should build a mockup, test it, and write a blog post about the experiment. –  Chris Cudmore May 17 '13 at 14:43
add comment

You could run both vent ducts to the same area and then install two vent caps side-by side. Your wall opening would have to be twice as big, but at least you would only have to do one cut, flashing, etc.

share|improve this answer
    
The problem with this, would be finding a vent cap. –  Tester101 May 17 '13 at 14:43
add comment