I am trying to blow out my sprinkler lines and I put together an adapter to connect the air compressor to the faucet pictured below. The air compressor was charged to 140PSI, and then I turned on a zone and opened the air compressor valve to 40PSI (into the faucet). But as far as I could tell, nothing was happening as far as water getting discharged from the system. It appeared that all of the air was flowing out of the pressure vacuum breaker.

The past couple of years I have hired someone to blow out the sprinkler lines and I know they attach to that faucet. I also know that when they are clearing the water from the system the sprinkler heads popup and the water discharges from them. So what am I doing wrong?

alt text

EDIT (2010-12-28): I am not sure why I was not able to blow out the lines through the pressure vacuum breaker (I imagine it is not sealing correctly as said by @gregmac is his answer) so I ended up installing a new valve beyond the PVB which is where I attached the air compressor.

alt text

share|improve this question
add comment

3 Answers 3

up vote 3 down vote accepted

My guess would be that there is something wrong with the backflow preventer. alt text

Most likely, the air inlet valve is not sealing properly. When pressurized from the side marked "normal flow" (which is where your tap is), it should open the check valve, and also force the air inlet valve shut.

It's probably a rubber gasket, and might be worn out and need to be replaced, or maybe something is physically holding it open. Try pushing on it to see if you can get it to close all the way. Some silicon grease around the gasket will help it form a good seal and prolong the life of the gasket.

share|improve this answer
add comment

Your pressure is probably too low to shut the backflow, so all of the air is coming out the PVB. You've got to get sufficient pressure to seal the PVB. Mine takes 50 - 60 psi using a compressor that delivers 6-7 CFM in that PSI range.

Also consider the professionals use compressors delivering much higher CFM...their compressor may be quite capable of closing the valve at 40psi.

share|improve this answer
    
John Blue''s answer is dead on. You need a lot of CFM and pressure to do the sprinkler evacuation job, with or without a backflow valve in the line. –  user12902 May 8 '13 at 15:31
    
In other words, professionals have humongous tanks of air and large compressors that require a trailer. It is not the pressure as much as volume of air. In fact, too much pressure can hurt components and running air for too long can overheat the sprinkler system. –  rjt May 12 at 22:24
add comment

I haven't done this work before so I don't have much to add, but did find this tutorial that mentions removing that backflow preventer before blowing out. Of course, then you'd need to make a new adapter since your faucet won't be connected to the system anymore. And this also doesn't explain why others have been able to do it in the past with the backflow preventer in place. Overall this is a pretty crap answer, sorry!