I have spent hours searching the web for information on this 20+ year old zone control panel, which supports 3 zones of Heat and A/C.

The thermostat I'm replacing (on Zone 3) connects to T4/T5/T6 as W, R, Y respectively (the wire colors do not match because it's sharing a cable with Zone 2, which go the matching colors). I need a C (Common) wire to supply power to the thermostat, and found 24VAC across M2 and T5 (M1/M2 are the power leads to the zone damper, and seem to be connected internally to "1" and "2", the 24VAC supply.

However, when I connect the C terminal on the thermostat to the M2 connection, there is a click from some of the zone relays and the transformer hums as if it's overloaded. I removed power after a few seconds and disconnected the wire (now hanging off to the right of the picture).

I've disconnected the wire from the C terminal at the thermostat, and measure 24VAC across it and the Rh terminal on the 'stat, so I don't believe the issue is in the wiring.

The thermostat is a Filtrete 3M50; I've read that it draws less than .1 Amp, so I don't think this should be enough to put the system over some maximum current draw.

I'm looking for ideas on how to troubleshoot this.

enter image description here

share|improve this question
1  
Do you have the wiring diagrams for the HVAC system, and the control panel? Don't forget, sometimes you can't use the latest and greatest technology with a 20+ year old system. This answer might be helpful. – Tester101 Mar 8 '13 at 14:08
    
No, it appears to date from the 80s, and I can't find anything that quite matches. – TomG Mar 8 '13 at 16:03
    
Every document I find on Honeywell MABS controllers, shows M1 as C. – Tester101 Mar 8 '13 at 16:10

I have just successfully installed a Honeywell RTH6500WF Wi-Fi Series thermostat on Zone 1 of my Mastertrol Mark V zone control system. I used a separate 120VAC to 24VAC transformer (AUX) with one lead of the AUX 24VAC hooked to Zone 1 terminal T5 of the Mark V panel (R terminal on the thermostat) and the second lead of the AUX 24VAC hooked to the wire (4th thermostat wire) that goes to C on the thermostat. A separate 24VAC transformer is required for each zone thermostat that needs a C connection.

share|improve this answer

It appears according to the manual for the Mastertrol Automatic Balancing System (MABS) EZ Zone (EZ-2 and EZ-4) Control Panels (PDF), that M1 is used for C.

enter image description here

enter image description here
Click for larger view

This does not appear to be the manual for your device, so this information may not be correct.

The manual for the MABS 2 Zone Panel (PDF), also shows M1 being used for C.

enter image description here


UPDATE:

After further review, you should be able to connect the C wire directly to the transformer terminals. Measure for Voltage between the T5 terminal of the zone you're working in, and the 1 and 2 terminals in the 24V 40VA Transformer section. One should measure 24 Volts, while the other measures 0 Volts. The one that gives you 24 Volts, should be able to be used as C.

share|improve this answer
    
@Tester- I've seen other comments pointing to M1, and one other person with the Mark V that couldn't get it to work on M1. Like them, I get 0V across T5 (thermostat's R) and M1, and 24V from T5 to M2. Perhaps there was a change made after the Mark V to the newer panels like you show. +1 for finding and including the diagrams. If a Mark V diagram doesn't surface, I may have to go with an external power supply. – TomG Mar 8 '13 at 17:16
    
@TomG After working on this question a possible solution to your problem has finally struck me. Please see the Update section of my answer, which hopefully helps. – Tester101 Oct 9 '14 at 13:43
    
@TomG I think you're right. I tried to contact Honeywell with no success, but looking at the wiring of others it appears M2 is more likely to be used as C on the Mark V. – Tester101 Oct 24 '14 at 13:24

Go to the transformer and see what wire is common, it will be opposite of RED going to the thermostat on R or Red. Common is the side of 24 v power that every 24 v circuit terminates upon to complete its path. You will read 24 volts across every wire with Red , only with a call for heat will white not read 24 volts to red from white as the switch between red and white will be closed in the stat. open switch will read 2 sides of power closed switches read only 1 leg of power.