Tell me more ×
I moved into a new house and never heard of this before, so I thought it was strange.
On 2 circuits I've had a GFCI trip, and when they do, they trip the entire circuit. I thought they were just for the specific GFCI outlet, not the entire circuit.
Do I need to rewire these, as they are nuisance tripping.
GFCI's tripping should not be treated as a nuisance: they are a safety device. If it's tripping, it means one of two things: there is current flowing out the ground (precisely the condition indicating a fault in something attached; this current could potentially flow out of the person using the device thus electrocuting them), or the GFCI is faulty. If the GFCI is faulty, it should be replaced. If a device being protected by the GFCI is faulty, then that device should be replaced. – gregmac Jan 14 at 21:01
1 Answer
up vote 4 down vote accepted
Yes this is correct; a GFCI will protect downstream loads. The purpose of this is that you only need a single GFCI outlet per circuit. Alternatively you could use a GFCI breaker, but these tend to be more expensive.
If this is not behavior you want and you can confirm that it is not needed for safety and code-compliance reasons (ie: it doesn't feed any downstream bathroom, kitchen or wet/damp location outlets), you can rewire the outlet with a pigtail instead of using the Load side of the outlet - the outlet will work as a standalone outlet and trips will not affect downstream loads.
Note, just because someone doesn't want that behavior doesn't mean they don't need it. If you rewire, make sure all receptacles that need GFCI coverage have it. – BMitch Jan 14 at 20:52
Thanks @BMitch, I've updated the answer to reflect this. – Steven Jan 14 at 21:11