I've managed to add a C wire to my thermostat. I then decided to check the voltage between the R and C wires, and find that it read as 27.8 volts, not the 24 volts it was supposed to be. Could this cause problems? I do have a Lux thermostat which is having trouble with it's ambient temperature reading, but I'm not sure if it's because of the voltage or something else.

share|improve this question
2  
Will it run correctly without the C wire connected (many will, at the expense of going through batteries quickly)? That would be a quick trouble-shooting step. What model is it? Maybe it has a rating somewhere that says eg "Acceptable input range: 22 to 26 VAC" –  gregmac Jan 8 '13 at 5:19
add comment

2 Answers

It's a bit high but whether it will be a problem depends on your thermostat and how it tolerates the high voltage. Also consider that the furnaces controller board is also receiving this voltage.

Before you start anything else, check to see if your thermostat can be calibrated and complete this step first.

To rule out the higher voltage as the cause of the faulty temperature reading, find another transformer that gives you close to 24VAC and connect it to R and C - basically use that power source instead of the transformer in the furnace. If the temperature reading is correct now then you have verified the cause. If other transformers are also giving higher than expected voltages, check your input line voltage - if that is high, so will the transformer output.

If line voltage is OK and other transformers are OK then you can replace the transformer in your furnace; it's a pretty straight forward replacement usually. Just remember to turn off the power to your furnace first!

share|improve this answer
3  
One common failure of the transformer in a furnace that results in a higher than normal voltage, assuming that the input line voltage is at the correct level, is shorts between adjacent turns or layers in the primary winding of the transformer. Shorted turns cause the turns ratio from primary to secondary to change and thus an output voltage change. For example if the line voltage is 120VAC the turns ratio of a functioning transformer would be 5:1 to get to 24VAC. If some portion of the turns were shorted the ratio could be reduced to 4.31:1 resulting in the 27.81VAC that you see. –  Michael Karas Jan 8 '13 at 6:18
add comment

Normal voltage range for 24 volt HVAC systems is 20 to 30 volts. Normally if you are in that range to the upper/lower bound of accuracy of your measuring equipment you're fine. An induction transformer will read higher when lightly loaded. All of them I've ever worked with over the years do this, even modern switched mode supplies have a lower bound under which they read higher than the nominal voltage. As always check with the equipment vendor if there are any doubts regarding range of voltage over which your equipment is expected to operate.