Now Smoke & Heat Detector is used for fire alarm.
NFPA 72, 2010 Edition, Chapter 29, Section 29.5.1 Required Detection,
states the following:
29.5.1.1 Where required by other governing laws, codes, or standards for a specific type of occupancy, approved single and
multiple-station smoke alarms shall be installed as follows:
(1) In all sleeping rooms and guest rooms
(2) Outside of each separate dwelling unit sleeping area, within
6.4 m (21 ft) of any door to a sleeping room, the distance measured along a path of travel
(3) On every level of a dwelling unit, including basements
(4) On every level of a residential board and care occupancy (small facility), including basements and excluding crawl spaces and
unfinished attics
(5) In the living area(s) of a guest suite
(6) In the living area(s) of a residential board and care occupancy (small facility)