Most of the info I have on code implies this would be OK, but one item I have says that a 1 1/2 vent can only serve 8 "non-WC" fixture units.
Tell me more
×
Home Improvement Stack Exchange is a question and answer site for
contractors and serious DIYers. It's 100% free, no registration required.
|
|
In California, which is based on UPC, a 1-1/2" vent, properly installed, can vent a 3" toilet drain. However, local codes can vary, so it's always a good idea to draw a diagram and get a permit, so they can inform you of any special rules or anything you may have missed. |
|||
|
|