As above, the hot water works but the radiators do not come on. It's an old gas powered central heating system. We're thinking it's the wall thermostat at fault but is there anything else it might be?
Update: I thought I should post a follow up for the sake of future Googlers.
It turned out to be the pump as ChrisF had suggested. The hot water still worked because it's gravity fed from the loft (or attic if you prefer ;)), whereas the pump wasn't kicking in at all. 20 years' worth of use had clogged it up. When the system was emptied the water that came out of it started brown and quickly went black.
With your car you get it serviced every year. Boilers get serviced on a regular basis too but the system itself doesn't, so over the years the muck builds up and builds up and nothing gets done about it causes something to break, i.e. now.
up vote 5 down vote accepted
The most obvious thing that springs to mind is that you have air in your system.
Do the pipes between the radiators get hot, or the bottoms of the radiators but not the top?
If so then you need to bleed your radiators. You should have a little key with a square hole. Carefully open the valve at the top of the radiator a very small amount - you should hear a hissing sound of air escaping. Wait until water starts to dribble out - use a cloth to catch this. Repeat for all radiators.
For more information, pictures and a couple of videos see The Ultimate Handyman
UPDATE
Turn your thermostat all the way up - to make sure that it registers the current temperature as too cold - then the boiler should kick in. If not then it's the thermostat. If the boiler does kick in check the central heating return pipe - this should get hot after a few minutes. If not then there's either an airlock in the pipes themselves or the pump isn't working.
Can you hear the pump turning. If not there's a screw head in the centre of the pump which controls the speed of the pump (see the pictures here). Turn this clockwise. If the pump still doesn't turn you may need to replace it.
It could also be the electronics in the boiler not sending the signal out to the pump.
At this point consulting a heating engineer would be your best option.
Hi Chris, thanks for your answer. We did have some issues with the radiators similar to how you describe and there is trapped air in there for sure. However, when we had those issues we did get some heat out of the radiators that had problems and some of them were completely fine whereas others had the problems. At present none of the radiators come on at all. – bcmcfc Sep 16 '10 at 10:03
My radiator system also has an extra sensor attached to the pipe -- basically, it won't run the pump unless it knows the system is hot. (so if something else goes wrong, it won't run the pump for no reason). Of course, it's yet another point of failure. – Joe Sep 16 '10 at 14:40
There should be a valve in line with the pipe that goes to the radiator. They are usually right after a manifold (one in, many out). The thermostat controls those valves. You can feel the pips (carefully) to see if the hot water gets past the valve. You could also check the voltage to the valve coming from the thermostat. They are usually 24 volts AC to open them and let the hot water through. Be sure to put the voltmete on AC not DC.
protected by BMitch Oct 17 '12 at 3:05
Thank you for your interest in this question. Because it has attracted low-quality or spam answers that had to be removed, posting an answer now requires 10 reputation on this site (the association bonus does not count).
Would you like to answer one of these unanswered questions instead?