So, next in my quest to evaluate the health of my new home's electrical system, and call in professionals if needed, was some voltage checking of the panels/outlets around the house. What I have is a main 200A service in the basement, and a 100amp sub-panel on the main floor. See the attached schematic (notice the main panel has a bonding strap between neutral and ground, where as the sub panel does not- I believe this is the right way for it to be wired).

I borrowed a friends Fluke multimeter and found the following- In both panels, the red bar to neutral is 119 volts, and the black bar to neutral is 121.5 volts (red and black in my diagram). Testing the outlets around upstairs, I noticed that, as expected, some have a delta v of 119, others, 121.5. I then tested the voltage drop across red to black, and found it to be around 242 volts. I also noticed that I have a slight voltage across my neutral to ground (it just so happens to be about 1.5 volts) upstairs.

Is this kind of small asymmetry normal? Should I be getting an electrician in to check things out?alt text

share|improve this question
    
The main thing I would check is the sizes of the wire going to your sub-panel –  Brad Gilbert Sep 15 '10 at 14:51
    
The wires between the two panels appear to be 4AWG. –  MarkD Sep 15 '10 at 15:52
add comment

1 Answer 1

up vote 12 down vote accepted

The panels are wired correctly. There must only be one connection between neutral and ground in the main service panel. I believe this is to prevent any current that would normally have gone through ground from being passed along the neutral wire between panels instead.

The differences in voltage between the two busses is fairly normal. It is likely caused by the transformer on the pole, or by a load in your house that is causing a voltage drop. For the latter you can try turning off circuits to see if it goes away, but for the former, you're pretty much SOL. That said, it's not a problem. Mains in North America is supposed to be 120V +/-5% (so 114 to 126V is acceptable).

The voltage from neutral-ground is also normal. Here is a decent (but technical) article on neutral-ground voltage. In short, it's caused by the fact that over any length of wire, you have some drop in voltage. Since no current flows in the ground wire, there is no drop there and thus you have a difference in voltage. Another source is induced current, which can be caused by wires going through magnetic fields, such as near motors.

In short, it doesn't sound like you have any problems.

share|improve this answer
    
Thanks for the great response/info Greg. I was hoping this would be the case. After all of the other gremlins I experienced over the last few weeks, I was hoping I had finally sorted it all out, and it appears I have. –  MarkD Sep 14 '10 at 14:12