I've moved into a house, and am fitting a series of 5 halogen downlights beneath a shelving unit. The wall on which I am fitting it previously had an uplighter. I removed this so now have exposed live, neutral and (unsheathed) earth wires on the wall. This is already operated by a light switch on another wall.

The new lights I have come with a fitted fused (3 amp) plug. The instructions say if it is installed directly on a lighting circuit it will need a 5 amp fuse.

So - if I want to wire it directly, can I assume the lighting circuit is adequately protected since it already had a light fixture (is this standard?), or for this fitting do I need to install an (unswitched) fused spur or something similar to add the 5 amp protection?


To clarify, the 5 halogen lights are wired into one fitting with a transformer leading to one plug.

share|improve this question
    
From the OP's profile, the location appears to be the UK. – Vebjorn Ljosa Aug 29 '12 at 8:54
    
Thanks Vebjorn - yes, Scotland. – waj Aug 29 '12 at 8:57
    
@Tester101 outside of a plug? In a spur then? Here's the product link (this might not be the exact model). Its instructions were a bit brief and I want to be sure. – waj Aug 29 '12 at 11:40
    
Not exactly. The plug itself is fused with 3A, which is then connected to the primary of the transformer. I want to remove the plug. Would these lights require a fuse when the previous did not, or is this just a precaution? – waj Aug 29 '12 at 12:52
    
@Tester101 thanks. So I can assume the lighting circuit isn't itself fused, that this is conventional and that the previous light was deliberately unfused? – waj Aug 29 '12 at 14:36
up vote 3 down vote accepted

Comments converted to answer.

If the manufacturer says they need a fuse, then I'd probably install a fuse. Just install a 5A fuse before the transformer, and make sure it's accessible in some way.

The light circuit is probably on a fuse/breaker at the service panel, but since you are using a transformer to step down to low voltage a fuse may be required to protect the transformer and low voltage wiring. The fuse/breaker in the main panel will probably be 15-20A; since it's designed to protect a normal line voltage lighting circuit, so you'll need another 5A fuse before the step down transformer to protect the transformer and everything downstream from it.

share|improve this answer
    
I will attach a 5 amp fuse, thanks @Tester101 – waj Aug 29 '12 at 16:33
    
@Tester101, what's the proper fuse holder to use in this situation? And does it go inside a junction box? – ArgentoSapiens Aug 29 '12 at 18:18
    
@ArgentoSapiens Not sure, I'd have to do some research on that. Typically there would be parts supplied with the equipment, if this was a typical/valid installation method. – Tester101 Aug 29 '12 at 19:26
    
@ArgentoSapiens I intend to use a fused spur (or FCU) and place it below my shelving unit. That way I have access to a plate with the fuse in case anything goes awry. They seem to generally be available with a 13A limit, which is more than enough for my needs. – waj Aug 30 '12 at 9:08
    
@waj: A fused connection unit (FCU) is probably appropriate but, to protect the wire to the transformer you should fit the FCU with a 3 (three) amp fuse (e.g. use the one from the plug you remove). The wire is sized for 3A but the lighting circuit can provide more than that, enough to start a fire in the wire to the transformer in the event of a fault. – RedGrittyBrick 7 hours ago