I am building a new full bathroom on what used to be my back porch. I am planning to extend the existing drain at a cleanout and to run it outside the house underneath the floor.

I need to know if I need to add a new vent to the extension, or if I can rely on the existing vent. The total length of the new (4") drain will be about 15' from the existing vent to the farthest fixture.

I am in Virginia. I've looked at the code but I can't figure out which rules apply to my situation.

Diagram of the drain

share|improve this question
add comment

4 Answers

up vote 7 down vote accepted

You must have a vent above the vertical run for these drains. As drawn, water from your new work cannot draw air behind it from your existing work.

This is what vents do: draw air in behind draining water.

You could functionally combine all the new work drains as drawn into a single vertical vent, but remember that it needs to be able to draw air from above their combined drain line.

Depending on your code you may or may not be able to combine these into a single vent, but they will need their own vent.

Drain Requirement

share|improve this answer
    
+1, otherwise the toilet would suck out the sink trap. –  BMitch Aug 17 '12 at 21:55
    
Thanks. Can I extend the new drain past the sink where it ends, and go vertical from there? Or use interior valves? Just so I know what the options are. –  mogrify Aug 17 '12 at 22:23
    
@mogrify so long as each drain has its own vertical vent through which it can draw adequate amount of air... –  Matthew Aug 17 '12 at 22:34
1  
Just to clarify, each fixture does not need their own individual vent. The Virginia code allows wet venting which would eliminate the need for the individual vents as you have shown. Wet venting is quicker to install and requires less materials. You can refer to my answer for more detail. –  pdd Aug 18 '12 at 4:22
add comment

You're very close to the thresholds for a vent based on distance. But as ppd explains, you cannot rely on the existing stack as your vent. One option, as others have suggested, is to individually vent each drain where it goes vertical in the wall, connect these vents in the ceiling, and tie that into the vent stack. Make sure you maintain a positive slope on the vent line. See pdd's post for a way to vent off the lavatory because of the vertical fall restriction, and a wet vent for the remaining drains.

trap distance table

906.2 Venting of fixture drains. The total fall in a fixture drain due to pipe slope shall not exceed the diameter of the fixture drain, nor shall the vent connection to a fixture drain, except for water closets, be below the weir of the trap.

Reference: Virginia building codes, plumbing, chapter 9 (vents)

share|improve this answer
    
(Edited) OK, so those are maximum slopes? I assumed they were minimums. I can maintain the slope except for about a 2' straight drop. –  mogrify Aug 17 '12 at 22:29
    
I suspect that's a required minimum, but there's also 906.2, which I'll add to my answer, that further limits how far the slope can go. –  BMitch Aug 17 '12 at 23:12
    
The distances you reference are for the maximum lengths of fixture drains/trap arms, which are measured from the trap to the vent connection, either dry or wet. There is no constraint on the distance of a wet vent itself. However, the existing vent could not act as a wet vent for the new bathroom as it is located downstream of the new bathroom and serves a bathroom on a different level. –  pdd Aug 18 '12 at 4:30
    
@pdd I'm confused, wouldn't a dry vent be the point after you separate off from the drain with a dedicated vent, and the wet vent would be that distance from the trap to the dry vent? Once you exceed the vertical fall or distance from the trap, you need a vent, and I'm not sure how that could be a wet vent. –  BMitch Aug 18 '12 at 12:13
1  
@BMitch you're correct on the dry vent definition, however the portion of pipe between the trap and the vent connection is not considered a wet vent, it is called the fixture drain. The length of a fixture drain is limited (as are the number of changes of direction). This limitation is based on the diameter of the pipe, as the fall on the fixture drain cannot exceed that of the diameter of the pipe. This distance is measured from the trap to the vent connection. The vent connection can be either a dry vent or a wet vent. Look at the drawings in my answer for what a wet vent is. –  pdd Aug 19 '12 at 0:51
show 1 more comment

I would like to clarify a few things regarding this question and the provided answers.

As others have stated, you will definitely need to provide additional venting for the fixtures within this new addition, the existing vent will not suffice. Others have recommended providing individual vents for each fixture and then combining them in the ceiling to one common vent. While there is nothing wrong with this solution, it is inefficient and would be more costly.

I'm not a licensed plumber in your state or country, (I am in Canada) I have reviewed your state's plumbing code. You are allowed to vent these fixtures with what is called a wet vent:

SECTION 909 WET VENTING 909.1 Horizontal wet vent permitted. Any combination of fixtures within two bathroom groups located on the same floor level is permitted to be vented by a horizontal wet vent. The wet vent shall be considered the vent for the fixtures and shall extend from the connection of the dry vent along the direction of the flow in the drain pipe to the most downstream fixture drain connection horizontal branch drain. Only the fixtures within the bathroom groups shall connect to the wet-vented horizontal branch drain. Any additional fixtures shall discharge downstream of the horizontal wet vent.

Source: 2006 Virginia Plumbing Code, Chapter 9 (starting at the bottom of page two)

This is possible because drainage systems are size so that the drain lines do not run full of water. The bottom portion is where the water runs and the top portion allows free air movement. (In the case of vertical pipes, water "clings" to the sides of the pipe as it moves in a spiral, this leaves the centre of the pipe open for air movement.)

In Canada, one of the rules to wet venting is that the water closet must be the last fixture connected to a wet vent, that is no other fixtures are allowed to be connected downstream of the water closet. This reason is that when the water closet is flushed it could "choke off" the wet vent of any downstream connections. I did not see any requirement for this in your code, however all of the sample drawings provided in Appendix N showed the water closet as the last fixture with the exception of Figure N4: B. Horizontal Wet Venting (page 4) which shows a shower connected downstream of the water closet.

Here are two isometric diagrams showing how your bathroom could be wet vented:

enter image description here

The one on the left shows the tub connected downstream of the water closet. The drawing on the right shows the water closet as the last fixture connected to the wet vent (this is how we would do it in Canada).

In both drawings, the red line represents the portion of the system which would be considered the wet vent. The dashed line represents the dry vent. As you can see, wet venting eliminates a lot of the vertical piping and saves on fittings as well. Please note that you should have a clean-out installed on the vertical section of pipe before the lav's fixture arm (located in the wall). This will allow for cleaning of the branch line.

share|improve this answer
    
This does looks like an easier solution than the individual vents; thanks for taking the time to review the code and add your answer! –  mogrify Aug 18 '12 at 14:14
    
You're welcome @mogrify. If it was me I would pipe it as shown in the right drawing as a fixture downstream of a water closet just doesn't feel right. –  pdd Aug 19 '12 at 0:57
add comment

The best way to go is for each fixture to have its own trap and vent, and add some cleanouts at the important junctions (keep the one at the wall, if you can access it).

I'd say you should definitely not try to just rely on the vent(s) of the existing bathroom.

share|improve this answer