I am renting a place where the only air conditioner is a window unit mounted in the wall in the main living area. The space in that main room is about 325 sq ft, and it has a 9 ft ceiling on average. The unit is a Frigidaire FAS182H2A1. It looks like it was manufactured in 1999, but I can't recognize any other useful specs on the partially worn labels. So, I don't know what its BTU rating is, and I couldn't seem to find the manual online.

Earlier in the spring, I felt it wasn't cooling well, and I took off the front panel to see that it was caked with about 1/8" of dust and pet hair from previous tenants. The landlord removed this, but the aluminum fins were still clogged with gunk. I tried the only thing that our local Home Depot had for this which was an aerosol can of foaming cleaner, so I sprayed and scrubbed for a couple days. It looks a lot better, but I am not certain the fins are really cleaned out. The air conditioner is still occasionally spitting out what looks like chunks of dried black gunk that has been displaced from between the fins.

Last week it was about 95 degrees F outside, and after several hours of this thing being turned on to its max level, the room cooled down to about 81 degrees (with all doors to other rooms closed). I used a thermometer I had to measure the temperature of the air coming out of the unit, which was between 67 and 68 degrees.

It's only getting hotter outside (ugh), so I'd like to try to do something about this. So, here are my actual questions:

  • How much cooling should I expect from this unit?
  • Is it properly sized for the space?
  • Is there anything I can do to improve its performance?
share|improve this question
    
Could the "H" in the model number be a "P"? I found a manual for "FAS182P2A1". –  Tester101 Jun 29 '12 at 16:58

2 Answers 2

up vote 5 down vote accepted

According to this, the Frigidaire FAS182H2A1 is an 18000 BTU device.
http://www.appliancepartsnationwide.com/FAS182H2A1/53279.htm

That's pretty powerful if working properly. The government suggests 8000 BTU for 325 SF.

http://www.energystar.gov/index.cfm?c=roomac.pr_properly_sized

Check your outside coils too and clean if needed. If that is not a problem it could be something internal. Some examples:

  1. partial clog in your expansion valve.
  2. low freon level

If cleaning the outside coils doesn't work, I do not expect repair to be practical. You can buy a new 10,000 BTU unit from Home Depot for $300. It would be reasonable to ask the owner to pay for it.

share|improve this answer

Just for clarification, there are two sets of fins. The inside ones and the outside ones. The outside ones will get caked with pollen, dust, dirt, bugs, etc and form a matte blocking air flow around the fins. Depending on where you live and how much the AC runs, you may need to clean this yearly. The best way is to open up the entire case and then get in there with water degreaser and a toothbrush to get all the gunk out.

Also, as Philip points out, that's a LOT Of BTUs for a very small space. If a unit is oversized, what will happen is that it will cool the space before it can dehumidify the space. So you end up with cold and damp...likely not something you want.

I'd second Philip and just go spend a few hundred bucks on a small 8000 btu unit.

share|improve this answer
    
Thanks... well, I would prefer that it cools the entire space, which is about 1000 sq ft. I typically keep all the doors open and the ceiling fans on in order to get better circulation. –  Chris Farmer Jun 29 '12 at 21:57
    
And it doesn't seem to be cooling too much, AFAICT. –  Chris Farmer Jun 29 '12 at 21:57
    
I just read it was made in '99. THat's a pretty old window unit. Not sure I'd put too much effort into working on it, but you could have a Sears tech come out to clean/recharge it if you wanted to. –  DA01 Jun 29 '12 at 22:14
    
Also, if you do end up replacing it (or your landlord does) you might want to consider two 10k btu units rather than one large 18k one. It'd be more efficient in cooling a divided space (not to mention easier to take in and out each season) –  DA01 Jun 29 '12 at 22:15
    
Make sure the fins have not been mashed together so air can get in. If so brush the fins lightly with a brass wire brush. –  lqlarry Jun 30 '12 at 0:38