Sign up ×
Home Improvement Stack Exchange is a question and answer site for contractors and serious DIYers. It's 100% free, no registration required.

Okay, when I first moved into the house, everything worked fine. After about a year, my garbage disposal stopped working. I thought maybe it was jammed but the blades still move when I turn the hex on the bottom. I just noticed tonight that if I reset this one outlet, and turn on the disposal switch, it trips the outlet. I tested this serveral times this evening. The disposal is plugged into another outlet under the sink, the outlet that trips is a different outlet. Any thoughts on what is going on and how this can be fixed??

share|improve this question
Unplug the disposal from its outlet, does the breaker still trip when you turn the switch on and off (obviously the disposal will not do anything because it is unplugged)? – auujay Jun 20 '12 at 23:14
Do you mean the circuit breaker in your power panel trips or the GFI in the outlet trips? – mikes Jun 21 '12 at 0:26
There's a metafilter thread with this same issue that you might find useful. If you are experiencing a real ground fault, you need to get it fixed by fixing the wiring, outlets, or garbage disposal. – Adam Davis Jun 21 '12 at 14:06

2 Answers 2

The receptacle that the disposal is plugged into is fed from the Load side of the GFCI receptacle, thereby providing ground fault protection to the receptacle. There is a ground fault somewhere between the GFCI and the disposal, which is causing the GFCI to do it's job and trip.

You'll have to locate the fault, and fix it. If you don't have (or know how to use) a multimeter, you'll want to contact an Electrician. If you have a multimeter and know how to use it, you can narrow down where the fault is by checking continuity between hot and ground.

Start by turning off the breaker, and insuring power is off in the area you'll be working. Unplug the disposal and do a continuity test between the hot blade (smaller blade) on the plug, and the ground pin (long roundish pin). If the test shows there is not fault in the disposal, move up the circuit to the next device (receptacle) and test again (don't plug the disposal back in). If you still haven't found the fault, continue working your way up the circuit (the switch next) until you reach the GFCI. If you still haven't found the fault, try replacing the GFCI receptacle (making sure to hook it back up the same way).

If you still cannot resolve the issue, it's probably best to call in an Electrician (since they'll have cooler gadgets to troubleshoot the circuit). I would focus most of my attention on the disposal and the switch, since those tend to be the usual culprits.

share|improve this answer

Your garbage disposal is wired through your GFCI outlet. This is generally not required by code*, and in fact motor based appliances can cause GFCI breakers to trip. This is why even though your washing machine is in a wet environment you don't use a GFCI for it - it may trip even when there's no ground fault condition due to the motor.

Generally as motors age they become more electrically noisy due to poor electrical contacts on the carbon brushes and contaminants on the brush contacts. This doesn't necessarily mean that continuing to use the garbage disposal is unsafe.

Further, even GFCI breakers age. It's quite possible that the garbage disposal hasn't changed at all, but the breaker has become more sensitive over time.

At any rate, you have a few steps for resolving this issue:

  • Replace the GFCI if you think the GFCI is going bad
  • Replace the garbage disposal and hope that the new one doesn't trip the GFCI
  • Have the garbage disposal re-wired to a new circuit without GFCI protection (it uses a good bit of current, so make sure it's not on a circuit with another large appliance like the refrigerator)

* Please check with an electrician familiar with your local code requirements

share|improve this answer
Motor load nuisance tripping is not as common with newer GFCI's, And most modern GFCI's fail open and will not reset if they have gone bad. – Tester101 Jun 21 '12 at 14:19

Your Answer


By posting your answer, you agree to the privacy policy and terms of service.

Not the answer you're looking for? Browse other questions tagged or ask your own question.