Why do I need all 4 wires in my generator twistlock?

The generator neutral and ground are bonded. I have installed a Siemens 3-pole transfer switch, but would prefer to use 3 wire extension from the generator to the transfer switch. (mainly cause the 4 wire is so big and bulky)

share|improve this question

3 Answers 3

This depends on whether your neutral-to-ground bonding is before or after the transfer switch. If the transfer switch is your service entrance, you can bond neutral to ground there (on the common side, after the switch, inside the transfer switch enclosure), and do switching only for the hot conductors. If neutral is bonded to ground before the transfer switch, then all points beyond the point of bonding are now 4-wire, and a transfer switch must switch both hots and also the neutral (not the ground wire).

You can't mix by having the utility power be one way (for example 4-wire) and the generator be another way (3-wire) because you can't switch the bonding. It has to be either both 3-wire or both 4-wire coming up to the transfer switch.

Edit: since you have bonding at the entrance and at the generator, you need to switch the neutral in the transfer switch. Because of that you need 4 wires from both sources in order to keep the neutral and ground separated so the two bondings are never connected together by more than one wire (it will be the ground wire).

share|improve this answer
    
The neutral to ground bonding is done at the entrance panel. The transfer switch and sub-panel are fed from the main panel via #8/3 and 40A breaker.The neutral buses float in the sub-panel. The neutral and hot wires are all switched. However the neutral and ground are bonded within the generator, per the label and Cdn. code reqts. for portable generators. I obviously can't connect the generator ground to the transfer switch ground, as this would cause double bonding. So, why can't I simply use the 2 hots and neutral from the gen, and not connect the ground? –  Dave Packer Feb 6 '12 at 14:32
    
The double bonding is why the neutral is switched in the transfer switch. The circuits in the subpanel fed from the transfer switch will have their effective bonding from whichever power source the switch choose. As in any other subpanel, neutral is kept separate from ground here. This all requires a 4-wire feed (edit: from each source) to keep things separated as they should be. –  Skaperen Feb 7 '12 at 23:17

I assume you are referring to a home installation, as it would be a somewhat different answer if this was in an industrial situation.

I believe you will find that neutral and ground are not bonded within the generator, therefore the 4 lines. The only place it should be bonded is at the Main Service Panel. The neutral is a current carrying conductor, ground is not! Lets say you have a high load (or short) that the Main panel sees. The neutral potential to ground can be as high as the Main voltage (120V or 220V)! If it were bonded at the generator and you were touching it at that instant, you're dead!

The ground is never switched by the transfer switch, only the main conductors (& sometimes neutral). I suggest you check the NEC and local codes before you proceed. Also do not bond neutral and ground at the transfer panel, or any sub panels!

This link shows the transfer switch wiring. It also says that some Transfer switches do not switch the neutral leg. Yours is three pole so it would.

EDIT: Please read Since yours has bonding at the Gen, and you are switching the neutral you're okay. This article expresses the same concerns I listed above.

share|improve this answer
    
Thanks, all! The neutral and ground are in fact bonded at the gen, per the label and as required for a portable generator (Canadian Elect code) The neutral is switched along with the red and black, and the grounds are not. –  Dave Packer Feb 6 '12 at 14:33
    
Please see my edit. –  SteveR Feb 6 '12 at 15:31

It's done just like your house. You only have 3 wires coming into house. The receptacle is probably a NEMA L14-30R our maybe 50 amp. At work we have a designated ground rod for our's which we attach to the frame. If it set up correctly coming in it will be set up correctly going out. Also you can't switch your neutral with the xfer switch.

share|improve this answer
    
Sorry, I'm having problems here. If my gen is bonded, I must switch the neutral. If unbonded, I don't need to, but I prefer to keep the gen bonded in case I want to use it as a portable unit. –  Dave Packer Feb 6 '12 at 14:32
    
Separate bonding at each power source, 4-wire feeds for both, switched neutral in the 3-pole transfer switch, and all grounds connected together, is the modern and safe way to do it (5-wire and 4-pole for those who have 3-phase). Your inlet will be as lqlarry says. –  Skaperen Feb 7 '12 at 23:27
    
Thanks much, folks. Connected and checked out by a very experienced electrician. Test run, all voltages and currents tested OK!! –  Dave Packer Feb 9 '12 at 1:06