We have one circuit breaker (40 ampere) in entry point of electricity line in our house, than we divided it into two separate line in two levels and put one circuit breaker( 32 ampere) in level one and other other circuit breaker (25 ampere) in level two.The main circuit breaker ( the 40 ampere) become automoticaly off every several hours, but other two circuit breakers ( the 32 ampere and the 25 ampere) don't become off.I am thinking that the distribution circuit breakers 32+25=57 is larger than 40 ampere, and it make the problem. Am I right? Should total of different circuit breakers in one system be less than the main circuit breaker?
|
|
Typically your master breaker is sized to be less then the sum of all of the sub breakers. The reason for this is in a typical house, you don't pull the maximum current from all branches at once. However, this setup does allow for the situation that you are running into where your master breaker can trip even though none of the sub breakers have tripped. There is nothing unsafe about this setup, but as I am sure you are aware, it can be very annoying to have the whole house loose power. In order to deal with this, you should look into what exactly it is that is happening to trip the main breaker. For example, is it the AC kicking on while a refrigerator is running? Or is there some other circumstance that causes the breaker to trip? Once you figure out what this situation is, you will know if it is possible to just avoid pulling too much power. If you do need to be able to pull more power, you will need to look into the specs of your distribution panel. It could be that it is not capable of handling more than 40 amps. Or potentially, depending on your location, the main service lines can't handle more than 40 amps. It is difficult to tell you what your situation can handle, but this is the path you will need to look into. |
|||
|
|
|
The two branch circuit breakers will trip if the load on their protected circuit is greater than 32 amperes, and 25 amperes respectively. However, since the main breaker trips at 40 amperes. If both branch circuits are pulling a full load the branch circuit breakers will not trip, but the combination of the loads will trip the main breaker (32 + 25 = 57 > 40 as you have said). It's a very common situation to have the branch circuit breakers total more than the main breaker, but this is almost never a problem since the circuits usually don't pull a full load. Remember, circuit breakers are there to protect the wires. They shut off the power if you are drawing enough power to damage the wire, so installing a larger main breaker is likely not an option (unless you contact your power company and have the service upgraded, which will include upgrading the feeder cable). Contact your local power company, and speak to them about a service upgrade. Other than plugging less stuff in, or cycling loads, there is not much you can do yourself in this situation. |
||||
|
|
|
There are 2 situations where the main breaker could trip before the branch breakers:
If you are experiencing a short in the system, you should address the cause of the short. |
|||
|
|