7

A neighbour is trying to sell me some of his leftover styrofoam insulation. I need to insulate my attic. Is styrofoam a good insulator, or should I use another type of insulation?

3 Answers 3

9

That styrofoam insulation will work, but it is not cheap per R-value (however it gives you a great R-value per inch). Insulating an attic usually means you have a lot of room for insulation and you will need high R-value so that is why the cheaper options are more popular (blown cellulose or blown fiberglass).

Said another way, if you have a couple of feet of space in your attic, you can just fill that all up with loose insulation and get R-45 (or whatever you need). But if you have a smaller space, say it is a finished room and the only space for insulation is between the 2x6 or 2x8s ceiling joists you may want to pay extra to get a higher R-value in that limited space.

1
  • 2
    +1 for the excellent point about R-value density of the styrofoam. I hadn't even considered that factor.
    – Doresoom
    Jun 13, 2011 at 19:12
8

There are two types of polystyrene (Styrofoam) insulation: expanded and extruded. The extruded type prevents the movement of moisture while the expanded type lets water through. The extruded type has better insulating properties (R-5/inch) versus expanded (R-4/inch). Both of these are going to give you more insulating ability per inch than a batt or loose-fill. However, they are likely more expensive per "R" than loose-fill insulation, and will be more difficult to install (since you'll need to seal their edges to either your rafters/studs or to each other.

You need to be very careful about how you engineer a vapor barrier into your walls/attic. You should only have one vapor barrier in your wall so that water cannot be trapped, causing mold to grow.

There are two different ways to insulate attics: vented and unvented. For vented, you ensure that air can move between your eves and the ridge or gables of your roof. You then put insulation at the floor of the attic. For most of the United States, you'll optionaly want to first put down a vapor barrier (such as plastic, kraft paper, or extruded polystyrene) between the ceiling joists, and then put a lot of vapor permeable insulation on top.

For an unvented roof, it's much more complicated. You first install a very large amount of non-permeable foam insulation it the rafters (above your head, in region 5, R-20 of insulation in order to prevent condensation), seal it with spray foam, and then attach an ignition barrier such as rock wool or drywall beneath the foam. And then, add enough vapor-permeable insulation to up the total R value to the required amount. This way, you don't need to provide any ventilation for that attic, and its temperature will be around the same temperature of your living space.

In summary, any foam board has a "good" R value per inch, but a "bad" R value per dollar, and with foam insulation it is tricky to install it in such a way that will not cause either moisture problems or cause your shingles to heat up and fail.

This corning page containing a table of recommended insulation values.

1
  • @BMitch, thanks! I'm going through the roof insulation process at my house currently. I found a cheap source of foam board, and am placing it against my roof decking, and foaming around it where accessible, and facing it with cellulose and fiberglass. My house is a cape-cod with no soffits and about eight isolated attic areas, many with no vents. Most of what I said was based on my reading of the 2012 International Residential Code.
    – Pigrew
    Sep 27, 2012 at 1:32
5

I'd opt for a different type of insulation. The styrofoam insulation that Home Depot carries is only rated for R-5 per inch. That means even a 2" thick piece will only give you R-10 for $0.96/sq. ft. I just insulated my attic this weekend with blown-in cellulose insulation, and achieved between R-30 to R-45 for about $0.42/sq. ft. (Note: I used 20 bags, which is the minimum purchase for a free 24 hour blower rental at both HD and Lowes.)

Be warned though, it is the messiest thing I've ever done. Be sure to wear a respirator with the appropriate filters. Don't skimp and use a cheap disposable dust mask. At one point it was so dusty in the attic that I couldn't see more than 10 ft. in front of me.

You could also go with the blown-in fiberglass insulation option, which is less dusty, but more expensive.

Or, as @B Mitch points out, you could go with R-30 fiberglass batts for $0.83/sq. ft.

6
  • Yes, cellulose is super messy. It works great for just blowing onto an attic floor for insulation. As messy as it was I would do it again for that. I would probably not do it in walls or anything where you try and fill a void in from a small hole.
    – auujay
    Jun 13, 2011 at 14:10
  • Don't forget the classic fiberglass batts. Relatively easy to work with, and temporarily relocate if you need to put a hole in the ceiling. Blown insulation also has a tendency to settle over time.
    – BMitch
    Jun 13, 2011 at 14:13
  • @auujay: as much of a pain as it is, blowing cellulose in via a hole in the wall is one of the least destructive ways to retrofit insulation into an existing home that I know of. Are there better options short of gutting the walls?
    – BMitch
    Jun 13, 2011 at 14:18
  • 1
    @ B Mitch- If I had to do that I would consider using the foam injected through small holes instead. Finished my 3rd floor into a bedroom I used cellulose in the walls and ceiling. In the walls it would easily fill about 1/2 of the void but then as it piled up inside the wall the air blowing from the hose just sprayed the celluose everywhere and it was hard to go all the way up to the ceiling with it.
    – auujay
    Jun 13, 2011 at 14:21
  • @B Mitch: I added your mention of using batts to the answer with a cost comparison. If you wanted to add your own answer, let me know and I'll delete the edit.
    – Doresoom
    Jun 13, 2011 at 14:46

Not the answer you're looking for? Browse other questions tagged or ask your own question.